Answer / carl_ellis
1) You can't calculate temperature from millivolts from a
thermocouple without cold junction compensation. The
thermocouple tables only apply when the reading is cold
junction compensated.
2) To determine temperature from a resistance value,
several data are required
- the type of RTD (Pt, nickel, copper)
- the temperature coefficient (the alpha) in Ohms/ohm/DegC
must be given - 0.00385? 0.00392?
- the RTD Standard, IEC, USDoD, DIN 43760 With the base and
the alpha tables are available on the web.
- the Ro, the nominal resistance at 0 deg C
The table you request is specific to the RTD in question.
No data, no table.
Carl Ellis
Measure First
| Is This Answer Correct ? | 0 Yes | 1 No |
how to calculate density?
why we use 3 wire rtd direct wiring for temperature measurement instead of temperature transmitter like bearing temperature
What is the difference between mmwc and mmwg?
How comparison of objects is done in PHP5?
how to calibrate and troubleshooting of leveltroll?
How does electro magnetic pump works ?
what is the input of digital counter during the the calibration time?
what is different between 2,3&4 wire rtd and how much maximum distance using plc to field.
How do understand by hart protocol?
4 Answers BW Instrumentation Electrical,
how to calibrate load cell
what is the output of conductivity sensor and PH sensor?
what is the difference between SCADA and DCS?
Civil Engineering (5086)
Mechanical Engineering (4456)
Electrical Engineering (16639)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)