why transformer calling in VA rating
Answers were Sorted based on User's Feedback
Answer / murali290
For any device the rating is given based on the losses occur
in it (loss is nothing but heat).In transformer 2 types of
losses occur 1.core losses: which depends on V &
2.cu losses: which depends on I only
but no losses depends on p.f.
therefore trasformer rating proportional to VI or VA
for large transformers the rating in kilo or mega ,hence
KVA or MVA
| Is This Answer Correct ? | 3 Yes | 1 No |
Answer / praha tuty
Transformer has copper loss & iron loss. copper loss occur
in windings & it is due to emf.Iron loss occur in core due
to current. so in order to measure the both losses,
transformer ratings are in VA rating.
| Is This Answer Correct ? | 0 Yes | 3 No |
Answer / rakesh maharjan
The KW rating is dependent on the power factor and power factor can be different depending the condition where as mostly 0.8, but if KVA rating is given we can calculate the KW rating as per our condition. So KVA rating is fixed and reliable to any malfunciton not to occur. so the transformer rating is given in KVA.
| Is This Answer Correct ? | 4 Yes | 7 No |
Answer / pramod attri
it's using step up, and step down at same frequency..by
mutual inductance.. it case transformer calling in kv,,,
| Is This Answer Correct ? | 0 Yes | 4 No |
Answer / rajeshambur
transformer have a two losses because open circut and short circut . two losses so transformer rating in va
| Is This Answer Correct ? | 1 Yes | 11 No |
what does vector group Dyn11 tell us? also tell me how will u differentiate between phase lead and phase lag thru this vector group
Why does not AC excitation use in rotor of AC Generator instead of DC excitation?
what is mean by induction & conduction principle ? how they differ from each other ? thank you
What do you mean by reverse current braking of an induction motor?
How many kw will suply from one db
Relation between Sq.mm of wire and Its current carrying capacity?
What is diversity factor and how to calculate it
2 Answers Al Faraa, Amul, Pentagon, Sobha Developers,
When i went to a interview the interviewer ask me a question for that i cant able to answer him if anyone knows answer me How will you design a capacitor bank for a plant? if my p.f is 0.6 i have to improve it to 0.9 or 1 what kind of steps i have to do? and is there any formula for calculating this?
Why the earth cable have current 1A - 2A , it is safety for Electrical system or earth cable should be zero amps ? how to troubleshoot?
How to calculate main incomer rating of APFC Panel ? Let's say i want to find main incomer for 11kV, 1000kVAR Panel.
TRANAFORMER RATING 500 KVA,33KV/433, SECONDARY SIDE SWITCHED ON ONLY CAPACITOR LOAD 140 AMS, PRIMARY SIDE HOW MUCH VOLTS INCREASE?
what is the advantage and disadvantage of billing in kwh and kvah by electricity board .
Civil Engineering (5086)
Mechanical Engineering (4456)
Electrical Engineering (16639)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)