why transformer calling in VA rating
Answers were Sorted based on User's Feedback
Answer / murali290
For any device the rating is given based on the losses occur
in it (loss is nothing but heat).In transformer 2 types of
losses occur 1.core losses: which depends on V &
2.cu losses: which depends on I only
but no losses depends on p.f.
therefore trasformer rating proportional to VI or VA
for large transformers the rating in kilo or mega ,hence
KVA or MVA
| Is This Answer Correct ? | 3 Yes | 1 No |
Answer / praha tuty
Transformer has copper loss & iron loss. copper loss occur
in windings & it is due to emf.Iron loss occur in core due
to current. so in order to measure the both losses,
transformer ratings are in VA rating.
| Is This Answer Correct ? | 0 Yes | 3 No |
Answer / rakesh maharjan
The KW rating is dependent on the power factor and power factor can be different depending the condition where as mostly 0.8, but if KVA rating is given we can calculate the KW rating as per our condition. So KVA rating is fixed and reliable to any malfunciton not to occur. so the transformer rating is given in KVA.
| Is This Answer Correct ? | 4 Yes | 7 No |
Answer / pramod attri
it's using step up, and step down at same frequency..by
mutual inductance.. it case transformer calling in kv,,,
| Is This Answer Correct ? | 0 Yes | 4 No |
Answer / rajeshambur
transformer have a two losses because open circut and short circut . two losses so transformer rating in va
| Is This Answer Correct ? | 1 Yes | 11 No |
Describe the test procedure to determine the vector group
why starter use to on a motor
How to test Alternator stability test for REF relay
Transformer Secondary maximum current (max. load)
what is mutual induction principle?
Stator of three phase induction motor creates Rotating Magnetic field.But why not Transformer?
3 phase supply is there Total kw 100 howmuch cable put the load
what is tesla ?
DC transmission
Sir we have 12.5 MVA(110/11KV) transformer (Y-Y) connected,which tripped showing earth fault,when we charged transformer it stood OK ,but on connecting 11 KV feeders it tripped showing earth fault.our service engineers found that the B phase and R phase phase connecting to neutral broken from HV OLTC(on load tap changer),and R phase and Neutral is ok.Dissolved gas analysis shows that accetline content is high,tan delta value is 12.My dout is it is an internal fault of transformer,why REF or diffrential relay is not acted?
why swityard is necessrry requirement in any bis power distributin systems?
what is the significance of positve n negative voltage regulation .on alternator
Civil Engineering (5086)
Mechanical Engineering (4456)
Electrical Engineering (16639)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)