3 phase supply is there Total kw 100 howmuch cable put the load
Answers were Sorted based on User's Feedback
Answer / khaled shaban
you have to calculate your ampere by using below equ.
I=P/Sqrt(3)*V*P.F
after that you have to select circuit breaker; after selection of CB check cable size referring to cable ratings as per manufacturer.
e.g. Volt 380V, with 100Kw and consider P.F=0.8
current will be 190A
cable should handle more than 190A, but first you have to choose MCCB for this load; the standard for your selection should be as following:
MCCB size = I*1.25 (1.25 at least)
so MCCB will be more than 237.5A (for standard MCCB you will select 250A)
hence your MCCB is 250A, your cable should be more than 250A.
As per cable manufacturer rating in my country, cable size should be (3*120+70)mm2 laid in duct, but in case if this cable laid in ground; cable size will be (3*90+50)mm2.
Is This Answer Correct ? | 4 Yes | 0 No |
Answer / g ravikanth
3core xlpe 95 sqmm or 3 x 120sqmm single core cable can be used.
Is This Answer Correct ? | 1 Yes | 0 No |
Answer / jithendra
For 100 KW for 150amp's load
125 SQmm copper cable or 185 SQmm Alummium cable
Is This Answer Correct ? | 1 Yes | 0 No |
How much CTs are required to measure th curent in DOL starting of motor?PLs explain.
How do you think they do earthing or grounding in ships and aeroplanes?
What is meant by H.R.C fuse?
40 Answers Gas Projects, GSCE, Taj Group,
What are the advantages of a three-phase system over a single-phase system?
Which is capital of Indian State Tripura ?
difference between over current and over load protection?
what is the minning of propotional, integral, derivative ?
actual rated capacity of a disc insulator??
HOW TO CALCULATE THE CABLE SIZE FOR POWER CABLE, CONTROL CABLE AND INSTRUMENT CABLE
What is mean by nominal voltage,Explain?.How much nominal voltage?.
Is phase preventer require when overload relay is there
what is the need of reactor in between the transmission line?..like powergrid like that..