Answer / ashish negi
the above calculation is correct but if we have to give our
demanded load to electricity dept. than the load should be
greater than the load as on starting motors , motors take 2-
3 times the full load cureent and at that time your MDI
(maximum demand index)will go beyond the calculated load.
so in that case your have to pay the penalty. so your
demanded load should be between 2500-3000 KVA.
| Is This Answer Correct ? | 5 Yes | 0 No |
Answer / rakesh maharjan
Remember the formula
KW=1.732 x V xI x PF
or
KW= KVA x PF, where PF = 0.8
connected load KW= Full load kw x 80%
Here in your case, connected load KW= 15000kw
so full load KW= 15000/80%=18750 KW
KVA= KW/.8
KVA=18750/.8=23437 KVA, this is the demand sanction.
I am junior Engineer.
Please verify by senior designer also.
| Is This Answer Correct ? | 5 Yes | 3 No |
Only the connected is mentioned and not the peak load.
Maximum demand is registered only if that apparent load
lingers for more than 15 to 30 minutes (as set).You have to
consider load factor(?) also .Apply for 12000 KVA MD
initially and you can apply for higher ,later.Once you get
the MD sanctioned, you can not get it reduced during the
agreement period.
| Is This Answer Correct ? | 1 Yes | 0 No |
What is breather? why we use it ?
which one is more costly:single phase induction motor or 3 phase induction motor??give proper reasons..
how do you measure earth leakages in 3phase wires?
What is meant by field loss in a DC motor?
Office , overtime and television how big this stage?
How can we find out LT UG cable fault (size,from-4*25mm sqr to 4*300mm sqr)? How mani types UG cable faults?
Seamless tubes are made by?
if single phase is having 220v supply then why three phase is having 440v instead of 660v?
when turbine trips generator will becomes induction motor or synchronous motor?
Discribe type of fault in DOL and stardelta startor.
what happened when we supply a dc current in dc motor?? can it worked properly?
hey guys i recently saw a long transmission line in which a sort of balloons in red and white color were hanging at each section.do u have any idea why are they kept for?
Civil Engineering (5086)
Mechanical Engineering (4456)
Electrical Engineering (16639)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)