If we have 15000kw connected load in a factory than how much
power demand sanction should be taken from electricity board.
Pls provide complete calculation.
Answers were Sorted based on User's Feedback
Answer / ashish negi
the above calculation is correct but if we have to give our
demanded load to electricity dept. than the load should be
greater than the load as on starting motors , motors take 2-
3 times the full load cureent and at that time your MDI
(maximum demand index)will go beyond the calculated load.
so in that case your have to pay the penalty. so your
demanded load should be between 2500-3000 KVA.
| Is This Answer Correct ? | 5 Yes | 0 No |
Answer / rakesh maharjan
Remember the formula
KW=1.732 x V xI x PF
or
KW= KVA x PF, where PF = 0.8
connected load KW= Full load kw x 80%
Here in your case, connected load KW= 15000kw
so full load KW= 15000/80%=18750 KW
KVA= KW/.8
KVA=18750/.8=23437 KVA, this is the demand sanction.
I am junior Engineer.
Please verify by senior designer also.
| Is This Answer Correct ? | 5 Yes | 3 No |
Only the connected is mentioned and not the peak load.
Maximum demand is registered only if that apparent load
lingers for more than 15 to 30 minutes (as set).You have to
consider load factor(?) also .Apply for 12000 KVA MD
initially and you can apply for higher ,later.Once you get
the MD sanctioned, you can not get it reduced during the
agreement period.
| Is This Answer Correct ? | 1 Yes | 0 No |
what is the d/f b/w iverter & converter.
i have 3500 amp load and select current transformer and perches.how i calculate .please understand
we all know that in capacitor there will be no ay physical connection between the two electrodes of the capacitor ,and the charge is stored between these electrodes during charging , so with out any physical connection how these charge is transferred from one plate to the another plate during the discharge?????
what r the advantage of selecting micro controller type tripping of circuit breaker than relay type tripping?
I have 12MW gas engine based power plant its running parallel with grid. my problem is When cpp run in island mode(without geb) that time geb transformer power factor is 0.2 lagging. When cpp run with parallel that time power factor is 0.94 lagging So how can i maintain power factor ofgeb transformer in island mode 0.9 lagging?
What is vacuum circuit breaker.define with cause and where be use it device?
I've heard that most of the substations are rated in multiples of 1.11 because of form factor.What is form factor?
Why ct secondary is not kept open while primary charged. Answer in terms of ct parameters.
WHAT WILL BE THE SPEED OF MOTOR IF NO.OF POLES ON STATOR ARE NOT EQUAL TO NO. OF POLES ON ROTOR.???
advantage and disadvantage of team work?
how the frequency was generated in power station
if a 3phase 100kva distribution transformer , 400 v,50 hz, 4-wire system is loaded at 160 k.w mostly 1-phase Lighting & Airconditioning split a.c load what will be the net effect on the power system in terms of voltage, powerfactor, current , efficiency of xformer
Civil Engineering (5086)
Mechanical Engineering (4453)
Electrical Engineering (16638)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)