Can anybody tell me what the breakdown voltage is for air
and what it is for transformer oil please?
Answers were Sorted based on User's Feedback
Answer / biswa
Breakdown voltage of air is 3 MV/m & for oil is 10-15 MV/m
| Is This Answer Correct ? | 4 Yes | 0 No |
Answer / sri
BDV of new oil should be more than 30 KV.Below 30 kv is not accepted
| Is This Answer Correct ? | 3 Yes | 0 No |
Answer / rax
the b/d strength of ir is 30kv/cm. the b/d strength of t/f oil depends on the voltage level of the t/r. for a 33/11 t/f the b/d should be above 55kv
| Is This Answer Correct ? | 1 Yes | 0 No |
Answer / tmc
Thank you, also if these two materials can withstand a high
MeV, what are the values for how high?
| Is This Answer Correct ? | 0 Yes | 0 No |
how many types of ct retio
With a phasor diagram show the effect of increasing the field current of a generator supplying a constant real power and connected to a grid system.
What will be the capacity of the generator set which can be used for my 2 ton window air conditioner ?
1. what is usage for power factor in industries?? 2.why we need to monitor power factor??
sir please send me techinical questions for junior engineer posting in bangalore railway i am diploma holder
What is the diffrence between ofline ups and online ups?
why you don not show protection and type of isolation in key single line diagram?
if an insulated power and control cables of a running gas diesel gensets laid direct in an open trench i.e, trench bed is not rcc of a power house in which rain water, spillage water alwas exists and all power control cables remains submerged even when gas gensets of 480 kw each runningin on load. These power &control cables runs from power house to switchgear room through these trenches in which water remains most of the time. pl explain its merit & de-merit
how does PLCC work?...
Can a 5 core cable one end with a 32A 3p+N+E plug and the other end 32A 3p+E be used on a generator?
how to calculate power loss cost of aluminium conductor and copper conductor?v=500v.i=100A.x-section area=68mm.squre conductor
We are installing a 1.6 MVA transformer at our crusher plant and the feeder of HPSEBL is 2 km away at substaion . and a VCB is installed in the substaion which is 2 km away from transformer so we need another VCB near the transformer.
Civil Engineering (5086)
Mechanical Engineering (4453)
Electrical Engineering (16638)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)