Why short circuit calculation is not required in LT cable
sizing and requiredin HT cable sizing only
Answers were Sorted based on User's Feedback
Answer / sudhanva madhukar mahamuni
Generally LT Cable size are not calculated based on Fault current basis, Due to High Fault current on LT System. For e.g. consider that 2500 kVA Transformer, %Z = 6.25%, 415 Volts at Secondary. Fault Current at Secondary system will be 55.64 kA. Now if we would have to select the Cable size based on Fault current then it would be ---
If √t
A = ----------------- Sq.mm --- For XLPE Cable Aluminum Conductor
0.094
585 sqmm, nearest standard rating of cable is 630 sqmm. Hence Commercially as well as laying point of view the same is not recommended nor as per good engineering practice.
HT Cable Sizing :
Cable sizing based on Fault current is possible In HT System, based practically and commercially point of view. Consider that 11kV system is feeding the power supply. As per IS 2026, 11kV Power system will have max 500MVA Fault Level. It means it will have 26 kA. 300sqmm cable will be sufficient to withstand 26 kA for 1 Sec.
Summary : System Design shall not be strictly as norms, it should be design considering Laying / installation, Practically and Commercially viable.
Regards
Sudhanva Madhukar Mahamuni
electricmahamuni@gmail.com
| Is This Answer Correct ? | 2 Yes | 2 No |
Answer / xyz
Short Circuit withstand capacity is to be checked for HT
cables. For LT breaker controlled motor feeders, the cable
impedance reduces short circuit current considerable, hence,
short circuit withstand capacity is not required to be
checked for the rated fault level of the LT motors.
| Is This Answer Correct ? | 3 Yes | 5 No |
What is Energy Audit..?
how many types of ct retio
what is power factor?
8 Answers Adani, Blue Star, Power Control,
What does dny11 stand for?
if the load is 80 amp for main fuse and 100 amp for breaker so how can we calculate the cable size (cooper ) .
hi all i like to know vat is power plot in control systems also i want to know abt latest trends in electrical & electronics
what is voltage, and how it makes the electron to move?
why we use ac supply as 415 volts instead of 415 v why we cant apply 230 v for dc
What is 100% protection of generator? Why 100% is not used but 95% is generally used?
how many hvdc lines in india???
what is the difference between online & offline caliberation of KWH meters. Can Digital meters be caliberated
what is the diff between earth leakage relay and earth fault relay?
Civil Engineering (5086)
Mechanical Engineering (4453)
Electrical Engineering (16638)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)