Why short circuit calculation is not required in LT cable
sizing and requiredin HT cable sizing only
Answers were Sorted based on User's Feedback
Answer / sudhanva madhukar mahamuni
Generally LT Cable size are not calculated based on Fault current basis, Due to High Fault current on LT System. For e.g. consider that 2500 kVA Transformer, %Z = 6.25%, 415 Volts at Secondary. Fault Current at Secondary system will be 55.64 kA. Now if we would have to select the Cable size based on Fault current then it would be ---
If √t
A = ----------------- Sq.mm --- For XLPE Cable Aluminum Conductor
0.094
585 sqmm, nearest standard rating of cable is 630 sqmm. Hence Commercially as well as laying point of view the same is not recommended nor as per good engineering practice.
HT Cable Sizing :
Cable sizing based on Fault current is possible In HT System, based practically and commercially point of view. Consider that 11kV system is feeding the power supply. As per IS 2026, 11kV Power system will have max 500MVA Fault Level. It means it will have 26 kA. 300sqmm cable will be sufficient to withstand 26 kA for 1 Sec.
Summary : System Design shall not be strictly as norms, it should be design considering Laying / installation, Practically and Commercially viable.
Regards
Sudhanva Madhukar Mahamuni
electricmahamuni@gmail.com
Is This Answer Correct ? | 2 Yes | 1 No |
Answer / xyz
Short Circuit withstand capacity is to be checked for HT
cables. For LT breaker controlled motor feeders, the cable
impedance reduces short circuit current considerable, hence,
short circuit withstand capacity is not required to be
checked for the rated fault level of the LT motors.
Is This Answer Correct ? | 3 Yes | 5 No |
what do you mean by plant earthing system.
function of apfc pannel
What is mean by hot and cold loop testing? What is the difference between them?
what is the use of interposed & reverse voltage transformer
basic priniciple of induction motor
what deffrence between KW $ KVA ?
How can we calculate C10 rating of a bttery from c5 or c20 ratings??
How many losses in generators? how we can reduce them? and also in motors,transformers?
If we are importing real power & exporting reactive power then what will be the effect on our system
can u name the different types of motors used in different types of applications?
Ceiling fan motor wiring Hi, I have 2 ceiling fans broken. The receiver/control units burned out due to lightening. One Harbor Breeze and one Hunter's I took them apart (remove receiver units). Now on both of the motor I see 4 wires coming out from each motor I really want to know the function of each wire. Are there anyway I can test to see which is which? After searching forums I know these 4 wires are from 2 sets of coils inside the motor, one is Start winding and the other is Runing winding I could not find the receiver/control unit any where, so I am planing to buy Capacitors and universal remote controls to make the fans run again. Anyone has any idea how to do the wiring, please help Thnks
Why only three phase power generation are load are used