Answer / sudhanva madhukar mahamuni
Generally LT Cable size are not calculated based on Fault current basis, Due to High Fault current on LT System. For e.g. consider that 2500 kVA Transformer, %Z = 6.25%, 415 Volts at Secondary. Fault Current at Secondary system will be 55.64 kA. Now if we would have to select the Cable size based on Fault current then it would be ---
If √t
A = ----------------- Sq.mm --- For XLPE Cable Aluminum Conductor
0.094
585 sqmm, nearest standard rating of cable is 630 sqmm. Hence Commercially as well as laying point of view the same is not recommended nor as per good engineering practice.
HT Cable Sizing :
Cable sizing based on Fault current is possible In HT System, based practically and commercially point of view. Consider that 11kV system is feeding the power supply. As per IS 2026, 11kV Power system will have max 500MVA Fault Level. It means it will have 26 kA. 300sqmm cable will be sufficient to withstand 26 kA for 1 Sec.
Summary : System Design shall not be strictly as norms, it should be design considering Laying / installation, Practically and Commercially viable.
Regards
Sudhanva Madhukar Mahamuni
electricmahamuni@gmail.com
| Is This Answer Correct ? | 2 Yes | 2 No |
Answer / xyz
Short Circuit withstand capacity is to be checked for HT
cables. For LT breaker controlled motor feeders, the cable
impedance reduces short circuit current considerable, hence,
short circuit withstand capacity is not required to be
checked for the rated fault level of the LT motors.
| Is This Answer Correct ? | 3 Yes | 5 No |
what is voltage ?
our industries ht line so power fluctation(once drop of power please rectify causes
how to calculate short circuit breaking capacity KA for 2500kva 33kv transformer.
What is the effect of atmospheric pressure & Temp; on efficiency of motor? Why NGR(Neutral Grounding Resistor) is used in 132/11 KV Transformer & how? What is the use of Auto T/F in Grid Station?
what is destructive and non-destructive testing of welding
How to calculate VCB rating for 33KV ,25 MW Power line?
what is meant by leading or lagging power factor?like in capacitor power factor is leading and in inductor power factor is lagging
SSC JE ELECT.
why do we use 25kv supply for traction purpose?
What the capacitor Current formula?, For 1 KVAr how amps its required? for using the KVAr for boosting the PF Design Calculation.( Eg: for 30 KVAr required how many KW?)
17 Answers Alstom, Call Centre, EDC, HCL, Procon Engineers,
how to calculate full load current of transformer & induction moter ?
In underground cables,we have a grading method called 'capacitance grading'.Why is it called 'capacitance grading' although we do not use any capacitor in it?
Civil Engineering (5086)
Mechanical Engineering (4456)
Electrical Engineering (16639)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)