WHAT IS THE USAGE OF Buckoltz relay IN POWER TRANSFORMER AND
AND HOW ITS FUNCTIONS?
Answers were Sorted based on User's Feedback
Answer / wasif
in case of fault enormous amout of heat is generated in the
main tank which decompose the oil as a result of which
gases are produced. When the gases travel from main tank to
conservator tank they causes the float of buchholz relay to
be inverted which in result makes the tripping contacts and
thus causes the breaker to be tripped.
| Is This Answer Correct ? | 7 Yes | 0 No |
Answer / nagaraja bagi
Buchholz relay is used for Transformer Internal faults,bcoz
of over load or internal faults more heat will produce it
decomposes the oil and produces the gas and because of
transformer insulation gas will produce and it will try
move from main tank to conservator bcoz it is light in
weight then alarm float will operate and gives the alarm if
it exceeds then tripping float will operate and trip the
Breaker of Transformer.
| Is This Answer Correct ? | 5 Yes | 0 No |
Answer / anant shetye
In power Transformer Gases form so before putting
Transformer in service we have to release that gases & LET
OIL SHOULD come to conservater tank for safe operation ,if
it is not do so and if you give supply to the transformer
Buckoltz relay gets trip & it provide safety to Transformer.
| Is This Answer Correct ? | 2 Yes | 1 No |
some practicle study shows that the reactive power at the receiving end is not equal to the reactive power at the sending end.But according to theory the reactive power is exchanged by different parts of the network – capacitors and reactors permanently, but is never consumed or produced. Then Where that reacrtive power loss occuring?is there any formula to calculate reactive power loss?
we have require a Motor (1500kW, 6.6kV, 50Hz) which shall operate at 1500rpm during 30min and after it shall run on 500rpm during 15min. The same cycle shall be repetitive during the whole working days. Which method is best and economic to achieve such type of task. VFD, VVFD, Pole changing motor etc.
What is the clear distance between a MV panel(rear side) and wall.
why transformer rating in always in KVA ?
how to select the double earth conductor if 21A full load?
How to select the different contactors ( starter combination) for different AC motors? what about fuse cappacity 4 different motors too?
why using 3 phase
what is the formula for converting KW into KWH ?
How to calculate load taken by a cable?
WHY WE CAN GENERATE POWER IN 3PHASE MODE ONLY NOT IN 4 OR 5 PHASE?
what is the constructional difference in generator if we want to genearate 6.6kv instead of 440v?
selection of conductor in different voltage?
Civil Engineering (5086)
Mechanical Engineering (4456)
Electrical Engineering (16639)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)