WHAT IS THE USAGE OF Buckoltz relay IN POWER TRANSFORMER AND
AND HOW ITS FUNCTIONS?
Answers were Sorted based on User's Feedback
Answer / wasif
in case of fault enormous amout of heat is generated in the
main tank which decompose the oil as a result of which
gases are produced. When the gases travel from main tank to
conservator tank they causes the float of buchholz relay to
be inverted which in result makes the tripping contacts and
thus causes the breaker to be tripped.
Is This Answer Correct ? | 7 Yes | 0 No |
Answer / nagaraja bagi
Buchholz relay is used for Transformer Internal faults,bcoz
of over load or internal faults more heat will produce it
decomposes the oil and produces the gas and because of
transformer insulation gas will produce and it will try
move from main tank to conservator bcoz it is light in
weight then alarm float will operate and gives the alarm if
it exceeds then tripping float will operate and trip the
Breaker of Transformer.
Is This Answer Correct ? | 5 Yes | 0 No |
Answer / anant shetye
In power Transformer Gases form so before putting
Transformer in service we have to release that gases & LET
OIL SHOULD come to conservater tank for safe operation ,if
it is not do so and if you give supply to the transformer
Buckoltz relay gets trip & it provide safety to Transformer.
Is This Answer Correct ? | 2 Yes | 1 No |
im working in one private compeny in gujarat. i was complet diploma electric in 2010 from gujarat technical board. now i want electric supervisor licence in gujarat but i dont't know when i apply? plz give me address of the licence dippartment office in gujarat. gandhinagar
What is meant by system?
what does happen if generator frequency fall in running condition & what should require immediately
when a three phase motor in running condition consumes 2A in each phase,and if one of the phase gets fails what will be the consumption in other two phases
In LRS how much water PH value maintain for good operation of motor?
why we do not switched on capicitor panel with DG Supply
What are linear and non-linear systems?
What is polar plot?
I did oil BDV test of 1600 KVA trafo 20KV/400V as per IEC 156. Result is 1) 58 KV 2) 58 KV 3)40 KV 4) 50 KV 5) 58 KV 6) 18 KV. Avr is 47 KV. Can we say oil is still ok even in the 6th test BDV is 18 KV ?
What does the temperature (30 deg or 35 deg celcius) mark on conservator of transformer indicates?
What is the basis for selecting Vk/2 or Vk/4 for REF and Differential protection of Transformer and What is the significance of magnetising current