I have a 33 KV sub stn with two mother transformers 33/11
KV of capacity 3150 and 1600 KVA respectively. The total
connected load 16809 KVA(11/0.433KV).how i calculate the
max current & how i decided the CMD.
Answers were Sorted based on User's Feedback
Ur tranformer not able to bear load coz total 4.75 mva are bear 83.125 amp current in 33 kv side and in 11 kv, 250 amp
But As per ur kva 16809 KVA DTC ur load current is 675 amp which is excess ( 100kva = 4 amp 11 kv side current )
| Is This Answer Correct ? | 0 Yes | 0 No |
What is the breakdown voltage?
What is the difference between grounding & earthing?
some ac motor's direction get change dueto ghanging input to the ac drives.(say ryb to rby). but some motor direction remains the same when phase sequence is changed fromdive side. can anybody guide me?
what will happen if dc supply is given to ac motor?
When we need up only in o/p 440v, so why we use directly in 11kva in input?
0 Answers Lupin, Medhaj Techno Concept,
How to the calculating the Reactive power ( kvar )
66kv under ground cable how to layaing in ground any special case two ckt r runing
how the speed decreases of a generator in power station if load increases
I have a reading off 1.5ohms at my mem my main c/b is rated at 40/6 amps in a domestic house and i was told to change it to a b curve c/b is this ok
What are the protections required in the main lt panel which is connected to the transformer.
HOW CAN I GET 5CORE HO7 CABLE SIZE IF I HAVE 1800A?
what is a FACTS devices? what is mean by STATCOM????
Civil Engineering (5086)
Mechanical Engineering (4456)
Electrical Engineering (16639)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)