Explain Three way boiler.
Answers were Sorted based on User's Feedback
Answer / malik shams-ul-arfeen
3 element control on boiler controls Drum Level through
control applied on feed water control valve.
3 elements are
1) Drum Level (Master)
2) Feed Water Flow.
3) Steam Flow.
Formula applied on it is. C = A - B.
Where,
C = Control output to Feed Water CV.
A = Feed Water Flow
B = Steam Flow.
U Can contact at msaarfeen@hotmail.com.
Is This Answer Correct ? | 5 Yes | 0 No |
Answer / vijayaprakash
question is not clear?
But i thought this is three element boiler drum level
controller.
this controller inputs having drum level, steam flow and
feed flow . it controls output feed water control valve.
Is This Answer Correct ? | 3 Yes | 3 No |
During valve sizing from all calculation you got flow coefficient CV 12,than what it means? like for selecting pressure transmitter if your MAWP is 12 bar than you select a capsule of max. 20 bar which cover your mawp 12 in same way for selecting control valve If CV is 12 than how we use it in selecting valve??????
Exapain Deatails of the PID controlller
1,why we use 4-20 ma output of all instrument qhy not use 0- 20, 2,what is the different between PLC & DCS. 3,how can we meaure maximum span of new flowmeter if not given any information.
How can I make calculation for Install level transmitter (DP) for open tank and cloes tank?
Can anyone explain in a simple way the difference between DCS and PLC?
Why do we go for 4-20mA? why not other standara?
how to convert % to ma
1 Answers Flour Tech Engineers (P) Ltd, Techint,
There are two chlorination tonners both are connected to two pressure swithes and the pressure switch is connected to SOV which operates the valve to changeover the tonner selection i.e if pressure one tonner goes low the other tonner should come in line if it is inautomatic selection design a circuit using relays ?
PLS TELL ME THE FUNCTION OR PRINCIPLE OF CREEP RELEIF VALVE..
If I installed wrong directions orifice plate then what showing value d.p transmitter?
Hi, Is there any smart plant instrumentation design training institute in Bangalore?
how u calibrate pneumatic n motorized c/v?