how to can we synchronize different capacity of DG
sets.60kva& 250kva?
Answers were Sorted based on User's Feedback
Answer / k.prakashchandra
Synchronization is as usual.The load sharing depends upon
fuel feed to prime movers
Is This Answer Correct ? | 2 Yes | 0 No |
Answer / kj
As per the previous answer, synchronising is not a problem.
Using a load sharing module which is set up correctly will
allow the sets to share the load on a percentage basis. In
other words if the load is say 200 kva the load would be
about 65% on each or 38 kva and 161 kva.
Is This Answer Correct ? | 2 Yes | 0 No |
What is Ton Capacity of Air Conditioner?
The insulation resistance of a cable can be measured by
How many types of circuit loads are there in a common electrical circuit?
HOW MANY EARTHINGS REQUIRED FOR GENERATER
Do you know how to measure the earth resistance? if so explain it
42 Answers ABB, BEL, BridgeStone, College School Exams Tests, Dalkia, Dalmia Group, DEC, Electrical, Genpact, HEC, IOCL, JLL, L&T, MSEB, Saraca, Sical, Telecommunications, University Exams,
3 shows a 415 V, 3-phase generator supplying a 3-phase 415/110 V transformer. Draw the individual and combined impedance diagrams to a base of 10 kVA. Determine the system fault kVA and the fault currents at the 415 V and 110 V busbars for short circuit faults on the transformer input or output terminals. Work in p.u. values of impedances.
Specify the crystal frequency required for an 8085 system to operate at 1.1MHz
Why the cost of CT increases with the decreasing of its CT Ratio (Technical Reason)?
can we use the 110 v primary Tr 240 v secondary step up Transformer as reverse 240 pri 110 sec
How to improve insulation resistance of Motor
how is the magnetic current test is different in delta-star and delta delta transformer.
What is the difference between Surge protection device and Lighting arrester?