Golgappa.net | Golgappa.org | BagIndia.net | BodyIndia.Com | CabIndia.net | CarsBikes.net | CarsBikes.org | CashIndia.net | ConsumerIndia.net | CookingIndia.net | DataIndia.net | DealIndia.net | EmailIndia.net | FirstTablet.com | FirstTourist.com | ForsaleIndia.net | IndiaBody.Com | IndiaCab.net | IndiaCash.net | IndiaModel.net | KidForum.net | OfficeIndia.net | PaysIndia.com | RestaurantIndia.net | RestaurantsIndia.net | SaleForum.net | SellForum.net | SoldIndia.com | StarIndia.net | TomatoCab.com | TomatoCabs.com | TownIndia.com
Interested to Buy Any Domain ? << Click Here >> for more details...


Why ues 250 ohms Resistor during hart type instruments
calibration with hart protocol in details ?

Answers were Sorted based on User's Feedback



Why ues 250 ohms Resistor during hart type instruments calibration with hart protocol in details ?..

Answer / s.k.bakshi

The 250 ohm resiatance is necessary to support the communication between transmitter and HART because it equalizes
1. loop resistance
2. barrier resistance
3.wire resistance
4. receivers resistance

Is This Answer Correct ?    15 Yes 7 No

Why ues 250 ohms Resistor during hart type instruments calibration with hart protocol in details ?..

Answer / anzal

WHILE USING COMMUNICATOR ITS NEED 250 OHM IN BETWEEN THE TRANSMITTER AND POWER SUPPLY......
THE COMMUNICATOR INJECT HIGH FREQUENCY IN LOOP FOR COMMUNICATING PURPOSE............
IN POWER SUPPLY USING LOW PASS FILTER...
LOW PASS FILTER ALOVE ONLY LOW FREQUENCY..HIGH FREQUENCY IT WILL BLOCK..........
THAT'S WHY IN BETWEEN 250 OHMS NEED...OTHERWISE IT WILL BLOCK THE HIGH FREQUENCY...IF HIGH FREQUENCY BLOCK IT CANNOT COMMUNICATE WITH TRANSMITTER..........

Is This Answer Correct ?    8 Yes 0 No

Why ues 250 ohms Resistor during hart type instruments calibration with hart protocol in details ?..

Answer / g.venkat

Because hart portocol need proper loop resistance

Is This Answer Correct ?    8 Yes 1 No

Why ues 250 ohms Resistor during hart type instruments calibration with hart protocol in details ?..

Answer / j shinde

For impedence matching.

Is This Answer Correct ?    5 Yes 1 No

Why ues 250 ohms Resistor during hart type instruments calibration with hart protocol in details ?..

Answer / carl_ellis

My friend Dan has an article on why HART needs a minimum
resistance in the loop to work.

http://blog.lesman.com/2011/10/06/add250-ohm-resistors-to-
make-hart-work/#more-68

Anzal, above, is on the right path. The loop power supply
is a low pass filter. The 1200Hz HART signal needs a
minimum resistance to develop a signal that the HART
receiver can 'see'.

Tell Dan Carl sent you.

Is This Answer Correct ?    1 Yes 1 No

Post New Answer

More Instrumentation Interview Questions

what is mass flow meter principal?

4 Answers   GIL,


yogokowa field bus system transmitter all's we are geting IOP fault in Contiunes please help me fine how we can normal the broblems?

4 Answers   ABB,


In RTU Panel we are having several Analogue & Digital Inputs /Outputs. We are recently facing some problems over Analog inputs , which are not updating properly (But Digital Input are updating normally) Can any one tell me from where the problem is creating , we have checked PLC CPU card, Analog Input card & we reconfigured ,But still the issue is there. Issue : 1. Sometimes Analog values are updating & sometimes not. 2. Analog values are not updating normally , showing some wrong Values 3. Total dead (0 value) Analog values are Level & flow measurement from the field instruments. (But in field the instruments are working normally & Displaying the values normally in local display unit) This problem we are facing in our Water Plant. If any one experienced this same problem or having any ideas related to our issue PLS send your valuable Answers/Replies...

6 Answers   L&T,


Which topics are covered in Process Control?

0 Answers   Honeywell, L&T,


in current transmitter why we use 4-20ma ???

2 Answers   IMCO, IOCL,


how to convert bar to mA?

1 Answers  


Pressure tx shows 1 mbar but we need 1000 mbar at this process condition .. how can we sort it out .

0 Answers  


how to calibrate transmitter online (in running plant)please explain correct procedure

4 Answers   Sabic,


I have a Control VAlve having size of 2 ".Only the known parameter is Pressure drop . Its 2 Kg. Then How to calculate control valve sizing means Cv.

0 Answers   JSW,


why flow transmitter showing 2.2ma?

2 Answers  


how to calibrate 0- 150 psi presure gauge by dead weght tester

0 Answers  


what is the formula for changing Range of Transmitter from X mmwc to some Y mmwc with respect to DCS NCMH flow range from x NCMH to y NCMH?

1 Answers   HCL,


Categories
  • Civil Engineering Interview Questions Civil Engineering (5086)
  • Mechanical Engineering Interview Questions Mechanical Engineering (4456)
  • Electrical Engineering Interview Questions Electrical Engineering (16639)
  • Electronics Communications Interview Questions Electronics Communications (3918)
  • Chemical Engineering Interview Questions Chemical Engineering (1095)
  • Aeronautical Engineering Interview Questions Aeronautical Engineering (239)
  • Bio Engineering Interview Questions Bio Engineering (96)
  • Metallurgy Interview Questions Metallurgy (361)
  • Industrial Engineering Interview Questions Industrial Engineering (259)
  • Instrumentation Interview Questions Instrumentation (3014)
  • Automobile Engineering Interview Questions Automobile Engineering (332)
  • Mechatronics Engineering Interview Questions Mechatronics Engineering (97)
  • Marine Engineering Interview Questions Marine Engineering (124)
  • Power Plant Engineering Interview Questions Power Plant Engineering (172)
  • Textile Engineering Interview Questions Textile Engineering (575)
  • Production Engineering Interview Questions Production Engineering (25)
  • Satellite Systems Engineering Interview Questions Satellite Systems Engineering (106)
  • Engineering AllOther Interview Questions Engineering AllOther (1379)