If a contactor need to replace with faulty one. what I want
to check?
Answers were Sorted based on User's Feedback
Answer / mani0786
its half wire series connection & phase sequence
Is This Answer Correct ? | 0 Yes | 0 No |
Answer / suga priya
simple multimeter is used to check for failure. The coil can become shorted, grounded, or open. The coil can become shorted when the insulation between the wires in the coil breaks down. This can be found by shutting off the power and taking a resistance reading between the terminals on the coil. The reading should be around 20 ohms, if it is significantly less, the contactor should be replaced
Is This Answer Correct ? | 0 Yes | 0 No |
can anyone provide me a amf panel control wiring using ec-2 relay?
What are operating procudures & Safety precautions to be observed while operating OLTC in manual mode ?
how to calculate a cable size while load is given in amp or kw and length is also define.?
A synchronous machines has higher capacity for (1) Leading power factor (2) Lagging power factor (3) Does not depend upon the power factor of machine (4) None of the above
could an induction motor be used for regenerative braking in electric-train control? in this type of application would some scheme have to be devised to obtain low synchronous speeds while braking? would induction-motor drive, therefore, be suitable for passenger service?
if 1hp jet motar drop voltage when start from 220v to 120v give the reason and solution.
Can we use Motor protection CB while we use the VFD for Speed control?? if not means please tell the reason!!!
What is the formula for finding fault level of generator?
what will happen if ac motor given dc supply?
why we do 2 types of earthing on tranformer ie:body earthing & nutral earthing , what is function. i am going to instal a 5oo kva tranformer & 380 kva DG set what should the earthing value
8 Answers Altrion Technologies,
how to calculate IR value of 33KV cable ??
which electrical supply used for long distance traction 1.1-ph 22kv a.c 50hz 2.2-ph 22kv a.c 50 hz 3.dc vtg 4.1-ph 22kv 150 jhz