how do we select a copper power cable for a 10 HP, 1440 rpm, 440V, 3 phase AC motor?..

Answer / yoyoma

These are the steps required to detemining the cable size
required for your motor.

1) Determine the FLA (full load amps) or FLC (full load
current) of the motor. This can be obtained from the
motor nameplate or datasheet. If these are not avaiable
refer to the charts in the NEC or CSA code books.

2) As per NEC and CSA the cable is to be sized a minimum of
an additional 25% of the rated FLA or FLC (FLAx1.25)

3) Next a derating factor may need to be applied for both
temperature and grouping of cable in a raceway or cable
tray. These should be found in your code books. Multiply
these factors to your answer from number 2 above.

4) Once you have done 1 through 3, you should have a
current value larger than that of the rated FLA or FLC
of the motor. Use this current value to select the cable
size that can handle this current.

5) Lastly, as a verification you must also determine if the
cable size selected in number 4 above is sized so that
the voltage drop is no less than 3% (some go as high as
5%) of the source voltage (in your case 4400V x 0.97 =
426.8V). If your cable is undersized then you must
continue to increase the size until the voltage drop is
within 3%.

6) Once these are all done, your cable will be sized
correctly and accounting for all additional factors.

Is This Answer Correct ?    3 Yes 0 No

how do we select a copper power cable for a 10 HP, 1440 rpm, 440V, 3 phase AC motor?..

Answer / wareagle

1. Determine the amperage for the 10 hp motor. You can do
this by looking at the NEC chart at this site.
http://www.electricmotorshop.net/index.php?
option=com_content&view=article&id=687&Itemid=352
2.From this chart the 10 HP requires 14 amps. You then go
to a wiring table and select the conductor that has an
ampacity of 14 amps or more. The local code will dictate
your selection.
3.This wire choice does not include voltage drop
requirements.You may need a large size to reduce voltage if
necessary.
4. local codes may dictate other requirements.

Is This Answer Correct ?    5 Yes 3 No

how do we select a copper power cable for a 10 HP, 1440 rpm, 440V, 3 phase AC motor?..

Answer / r k choudhary

first we have to find out the ampere then as per cable
sizing chart select the cable but one thing always kept in
mind that for safe working (losses ,voltage drop,efficiency
of motor) consider somthing extra size of cable.

Is This Answer Correct ?    1 Yes 1 No

how do we select a copper power cable for a 10 HP, 1440 rpm, 440V, 3 phase AC motor?..

Answer / sudhakar

depending on the current rating of the motor only we will
choose the cable rating and consider the current density of
the copper also important

Is This Answer Correct ?    2 Yes 3 No

Post New Answer

More Electrical Engineering Interview Questions

does over charging of a battery reduce its life?

4 Answers   KSEB,


How to calculate the cross section area for a 350 m cable, motor power is 26 kw???

1 Answers   Orient,


Is it really necessary to have reactive power in transmission line to transfer the power from one place to other?

3 Answers   Power Grid,


In an electrical conductor, if current flows because of flow of electrons, then why not the conductor gets thinner day by day???

1 Answers  


what is the total power generation in india?

1 Answers   GUVNL, HAL,


What is nyquist contour?

1 Answers  


What happens if we give the supply to the rotor of induction motor and make its terminal shorted?

3 Answers  


does meager test perform on lightning arrester ? if doesn't then why ?

1 Answers  


If 11 KV breaker on the primary side of a 11 KV/3.3 KV 12.5 MVA transformer can be installed at a distance of 1000 mtrs through a 11 KV cable. If no what are the probable reasons.

1 Answers  


why we are using Load factor?

1 Answers  


For these 2 devices what their power ratings are ? 1) single phase : AC 220V & starting amps 3Amps (i.e. starting torque) and the stabilized amps 2A ... For deep freezer 2) single phase : AC 220V & starting amps 2.7Amps (i.e. including the starting torque of a CRT monitor) and the stabilized amps 1 Amps thanks

1 Answers  


best manufacturer for busbar for outdoor switchyard having double bus bar scheme, can any one share technical specification of busbar. 132kv voltage ?

1 Answers  


Categories
  • Civil Engineering Interview Questions Civil Engineering (5086)
  • Mechanical Engineering Interview Questions Mechanical Engineering (4453)
  • Electrical Engineering Interview Questions Electrical Engineering (16638)
  • Electronics Communications Interview Questions Electronics Communications (3918)
  • Chemical Engineering Interview Questions Chemical Engineering (1095)
  • Aeronautical Engineering Interview Questions Aeronautical Engineering (239)
  • Bio Engineering Interview Questions Bio Engineering (96)
  • Metallurgy Interview Questions Metallurgy (361)
  • Industrial Engineering Interview Questions Industrial Engineering (259)
  • Instrumentation Interview Questions Instrumentation (3014)
  • Automobile Engineering Interview Questions Automobile Engineering (332)
  • Mechatronics Engineering Interview Questions Mechatronics Engineering (97)
  • Marine Engineering Interview Questions Marine Engineering (124)
  • Power Plant Engineering Interview Questions Power Plant Engineering (172)
  • Textile Engineering Interview Questions Textile Engineering (575)
  • Production Engineering Interview Questions Production Engineering (25)
  • Satellite Systems Engineering Interview Questions Satellite Systems Engineering (106)
  • Engineering AllOther Interview Questions Engineering AllOther (1379)