what is the breakdown voltage value in BDV test in
transformers?
Answers were Sorted based on User's Feedback
Answer / sudhansu kumar dalei
The BDV of oil in transformer is 60 KV/1 min within the gap
of 2.5mm in the test vessel of oil test kit.
| Is This Answer Correct ? | 77 Yes | 10 No |
Answer / rajesh kumar.k
As per IE rule it should withstand 40kv/min.
| Is This Answer Correct ? | 39 Yes | 12 No |
Answer / yog111283
as per rule. after oil filteration oil sparking value must
be more than or at list 60 kv
| Is This Answer Correct ? | 30 Yes | 12 No |
Answer / kishore
the minimum aceptable value of breakdown voltage in BDV
test is >30KV
| Is This Answer Correct ? | 15 Yes | 6 No |
Answer / nitin arora
It depends on the voltage rating of the transformer
IF transformer rating is less than 72 KV then minimum BDV should be 30 KV.
IF transformer rating is 72 to 170 KV then minimum BDV should be 40 KV.
IF transformer rating is more than 170 KV then minimum BDV should be 50 KV.
All above results are referring the 2.5 MM gap during test.
| Is This Answer Correct ? | 6 Yes | 0 No |
For veryfication of oil purity every year to be checked the
BDV(breakdown voltage),we have take out the transformer
oil in the transformer and collect in the high voltage kit
inthe kit two stem will be there within the 2mm gap and
then apply the high voltage 50kv for 1 minute and it
shiould be withstand upto the mentioned time.Otherwise oil
to be filtered.
| Is This Answer Correct ? | 24 Yes | 38 No |
Can anyone explain me about the RLC based Impulse high voltage generator and how to and operation of Series resonant High voltage reactor...?
brief notes on ammeters
what's mean by Transient stability analysis?
what is errection pcbs?
Any one Give me formula for to increse the power factor, 0.8 to 0.95, How much the KVAr Required
9 Answers Emerson, Rajshree Sugars, Siemens,
WHAT IS THE SHOPE TESTING
what happens when back charging of transformer is done for longer period
I have a 3 phase 600 volt prim. feed and a 120/208 sec. Isolateing tranformer .We are using this system for safety against shock . What is the proper grounding ?? Does the common on sec. get earth ground ???
It is advisable 2 use auto-transformer if transformation ratio is-a)110KV/11KV,b)230kv/110kv,c)110kv/66kv,d) 400kv/230kv
how u calculate ups battery backup
in star-delta tranformer,if the input of star connection is 400/7v 3 kva then what is the output of delta connection?
What is “pu” in electrical engineering?
Civil Engineering (5086)
Mechanical Engineering (4453)
Electrical Engineering (16638)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)