what is the breakdown voltage value in BDV test in
transformers?
Answers were Sorted based on User's Feedback
Answer / sudhansu kumar dalei
The BDV of oil in transformer is 60 KV/1 min within the gap
of 2.5mm in the test vessel of oil test kit.
| Is This Answer Correct ? | 77 Yes | 10 No |
Answer / rajesh kumar.k
As per IE rule it should withstand 40kv/min.
| Is This Answer Correct ? | 39 Yes | 12 No |
Answer / yog111283
as per rule. after oil filteration oil sparking value must
be more than or at list 60 kv
| Is This Answer Correct ? | 30 Yes | 12 No |
Answer / kishore
the minimum aceptable value of breakdown voltage in BDV
test is >30KV
| Is This Answer Correct ? | 15 Yes | 6 No |
Answer / nitin arora
It depends on the voltage rating of the transformer
IF transformer rating is less than 72 KV then minimum BDV should be 30 KV.
IF transformer rating is 72 to 170 KV then minimum BDV should be 40 KV.
IF transformer rating is more than 170 KV then minimum BDV should be 50 KV.
All above results are referring the 2.5 MM gap during test.
| Is This Answer Correct ? | 6 Yes | 0 No |
For veryfication of oil purity every year to be checked the
BDV(breakdown voltage),we have take out the transformer
oil in the transformer and collect in the high voltage kit
inthe kit two stem will be there within the 2mm gap and
then apply the high voltage 50kv for 1 minute and it
shiould be withstand upto the mentioned time.Otherwise oil
to be filtered.
| Is This Answer Correct ? | 24 Yes | 38 No |
what is the working principle of soft-starter & how it diff. from VFD ?????????
What are the safeties in elevators?what is the use of governor in elevator?
What is annunciator ?
What are the different lines and what are the different types of losses occur on them?
make control wire diagram of start and stop a function with a single push button
why DC source is used to idetify the polarity of CT/PT?
Hod do u calculate cable size for underground laying and the factors effecting/influencing it??
what is the use of earthing?
what is exiter winding,stator winding,avr?how it will work?
What are the characteristics of negative feedback?
750kva 11/415kv transformer having percentage impedence is5.64%. 11KV HV whose current 39.37A and 415V LV whose current 1043.43A.resistance is 2.5ohm. find no load loss and full load loss?
what r the checklist while installing a 380 kva DG set
Civil Engineering (5086)
Mechanical Engineering (4456)
Electrical Engineering (16639)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)