If the maximum demand is 120 KVA in a building, then what is
the Current taken according to load given ? Formula for it ?
Answers were Sorted based on User's Feedback
Answer / jose
120 kva means you have to supply 3 phase load.
3 phase load with 415 v and unity pf can take a current
according to eqn kva=1.732*Kv*I
I=120*1000/(415*1)=290 A appr
| Is This Answer Correct ? | 6 Yes | 0 No |
a Generator of 1KVA can supply upto 1.4 amps, so the maximum load could be 1.4*120
| Is This Answer Correct ? | 2 Yes | 1 No |
how much amps will get from a 360/11kv line
Give me clear explanation.What is the Different Between Load break switch and Vacuum circuit breaker
briefly explain principle of resistance welding
What are PLC leader logic program method
HOW TO CALCULATE THE SIZE OF CABLE COPPER & ALUMINIUM
11 Answers Amman Try, Prestige,
what is open star connection or open delta.
what is the diference between base speed and rated speed in motor
What is the relay function?
I have a transformer 3phase 11kv/410v and its name plate missing. now how can I judge its rated kva?
what is ph test in coolent cheking
In a d.c circuit, if current and resistance are known, power (P=I*I*R) can be determined. This relationship also applied to an a.c circuit. Comment the reason for this.
why current is leading in capacitor?
Civil Engineering (5086)
Mechanical Engineering (4456)
Electrical Engineering (16639)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)