Answer / jose
120 kva means you have to supply 3 phase load.
3 phase load with 415 v and unity pf can take a current
according to eqn kva=1.732*Kv*I
I=120*1000/(415*1)=290 A appr
| Is This Answer Correct ? | 6 Yes | 0 No |
a Generator of 1KVA can supply upto 1.4 amps, so the maximum load could be 1.4*120
| Is This Answer Correct ? | 2 Yes | 1 No |
From stability point of view,What(higher/lower) should be the value of inertia constant of rotating machines?
What happens if we give the supply to the rotor of induction motor and make its terminal shorted?
what are the affects of loose connection in electrical circuit.
why the voltage and current in a long transmission line are called travelling wave?
why+ve is earthed in electrostatic precipitator in thermal power plant
Explain principle of Soft-starter & how its working???
How does cost of generation from hydropower plant compare with other sources of electricity?
what is function of reactor coil in Power factor correction panel
In tranformer winding Connection Like Dyn1 ,so LV lags Hv by 30 deg and Dyn11 LV lead HV by 30,so how do this lagging and leading afffect the transformer??
why transformer rating is mentioned in kva?
what is induction relay
WHAT IS SHORT CIRCUIT STRENGTH OF 100 AMPS MCCB?
Civil Engineering (5086)
Mechanical Engineering (4456)
Electrical Engineering (16639)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)