How to select Main CB Rating for 220 KW Load?
Answers were Sorted based on User's Feedback
before the selection,first we should know that it is single
phase or three phase load.in case 1-phase we use p=vicosф to
find out the load current but in 3-phase we use p=√3vicosф.
suppose it's 3-phase then load current=382amp.now add
minimum 25% safety factor to it.then it will be 475amp ,so
we can select C.B of 500amp current rating.
| Is This Answer Correct ? | 7 Yes | 1 No |
Answer / sennapparajan
for 220kw load curent is 380 amps. so your breaker should
be min 1.5 times of full load current. so u can select 630A
breaker.
| Is This Answer Correct ? | 5 Yes | 3 No |
why does spark appears when we swith on the light
what is the difference between H.T Or HV lines...?
We have two parts in generator, electrical & mechanical. how it works?
what are the names and size of various conductors used in transmission lines
what's the difference between induction generator and synchronous generator?
IR value for 30kw lt motor
Isolation transformer primary to sec turns ratio?
help me with the question that might be ask on the interview for technical position
How to calculate cable size in HT AND LT
How open delta used for protection?
wat is d diffr btw shunt coil and trip coil in VCB?
Why power genaration in India is at 50HZ while America its 60HZ
Civil Engineering (5086)
Mechanical Engineering (4456)
Electrical Engineering (16639)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)