how to calculate cable size, olr rating, contactor rating
and mccb rating,to below given details three phase motor
75 kw,415 v,.85 pf,50 hz?
Answers were Sorted based on User's Feedback
Answer / brakadeesh
motor rating 75kw,so it taken full load p=1.732*v*I*cosfy
i= p/1.732*v*cosfy
=123 amp. so we requared a cable to carry 123 amp
contonious rating. so require to run motor in star delta
starter . in star delta connection load current is 58% of
line current. we require 58% of 123 amp carring capasity
cable.it is around 71 amp.generly copper cable taking 4
times current of cable rating and alluminium cable taken
1.5 times of cable ratting .so for 71 amp carring alu.
cable 50mm2 suffisent but due to high starting curent its
take 70 mm2 cable ib best.
its overload relay ratting is in range to 71 amp. it to be
60-80 amp,and mccb rating is 2.5 times of full load =200
amp
is best.
| Is This Answer Correct ? | 50 Yes | 35 No |
Answer / pvr.parthasarathi
75 Kw motor takes 134 amps full load current. But for
selecting its Cable, Contactor, OLR and MCCB, we have to
consider many other factors such as need of its operation.
Place of the Motor Control Centre and possibility of laying
the cable Wheter inside the duct, underground or in the
air. For selection of the Contactor enclosure of the
panel, its environments etc are to be taken into
consideration. So giving answer at a stretch basing on
some thumb rule is not technically qualified.
Other particulars are required.
| Is This Answer Correct ? | 19 Yes | 5 No |
Answer / v.raguvaran
THE MOTOR AMP IS 130AMP.THE CABLE(USE COPPER ) SIZE SHOULD BE 45sq.mm (delta connection),35sq.mm(star delta)
OLR RATING IS (125-135) BUT STANDARD SIZE IS (130-175)ABB
CONTACTOR RATING IS 200A(DELTA),100(MAIN)-100(DELTA)-50(STAR)
MCCB RATING IS 250A
| Is This Answer Correct ? | 0 Yes | 0 No |
i know> but my nglish not well> because of that i can not answer
| Is This Answer Correct ? | 1 Yes | 4 No |
Answer / rsbangra
motor rating 75kw,so it taken full load p=1.732*v*I*cosfy
i= p/1.732*v*cosfy
=123 amp. so we requared a cable to carry 123 amp
contonious rating. so require to run motor in star delta
starter . in star delta connection load current is 58% of
line current. we require 58% of 123 amp carring capasity
cable.it is around 71 amp.generly copper cable taking 4
times current of cable rating and alluminium cable taken
1.5 times of cable ratting .so for 71 amp carring alu.
cable 50mm2 suffisent but due to high starting curent its
take 70 mm2 cable ib best.
its overload relay ratting is in range to 71 amp. it to be
60-80 amp,and mccb rating is 2.5 times of full load =300amp
is best.
| Is This Answer Correct ? | 47 Yes | 57 No |
i need project topics along with circuit diagram in the electrical and electronics engg and also some websites regarding projets.
can we use generator(a.c) as a motor.if so how if not why.
What is restricted earth fault protection ?
What are the applications of different multistage amplifiers?Plz also write advantages of these amplifiers? Thaaaaaaaaanx
WHAT ARE THE DATAS REQUIRED FOR SCS SIGNAL LIST PREPARATION?
what is the different beetween kva and kwh?
please send previous exams question papers
I want to know the 'Test voltage' for Tandelta testing of 3.3 / 6.6 / 11 KV Motors. Please explain
electrical
The mechanical angle is electrical angle A always less than B greater than or equal to C equal to D less than or eaual to
How to check it good or bad capacitor
What is the work of ACCP in LT panel?
Civil Engineering (5086)
Mechanical Engineering (4456)
Electrical Engineering (16639)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)