Golgappa.net | Golgappa.org | BagIndia.net | BodyIndia.Com | CabIndia.net | CarsBikes.net | CarsBikes.org | CashIndia.net | ConsumerIndia.net | CookingIndia.net | DataIndia.net | DealIndia.net | EmailIndia.net | FirstTablet.com | FirstTourist.com | ForsaleIndia.net | IndiaBody.Com | IndiaCab.net | IndiaCash.net | IndiaModel.net | KidForum.net | OfficeIndia.net | PaysIndia.com | RestaurantIndia.net | RestaurantsIndia.net | SaleForum.net | SellForum.net | SoldIndia.com | StarIndia.net | TomatoCab.com | TomatoCabs.com | TownIndia.com
Interested to Buy Any Domain ? << Click Here >> for more details...


how to calculate cable size, olr rating, contactor rating
and mccb rating,to below given details three phase motor
75 kw,415 v,.85 pf,50 hz?

Answers were Sorted based on User's Feedback



how to calculate cable size, olr rating, contactor rating and mccb rating,to below given details t..

Answer / brakadeesh

motor rating 75kw,so it taken full load p=1.732*v*I*cosfy
i= p/1.732*v*cosfy
=123 amp. so we requared a cable to carry 123 amp
contonious rating. so require to run motor in star delta
starter . in star delta connection load current is 58% of
line current. we require 58% of 123 amp carring capasity
cable.it is around 71 amp.generly copper cable taking 4
times current of cable rating and alluminium cable taken
1.5 times of cable ratting .so for 71 amp carring alu.
cable 50mm2 suffisent but due to high starting curent its
take 70 mm2 cable ib best.
its overload relay ratting is in range to 71 amp. it to be
60-80 amp,and mccb rating is 2.5 times of full load =200
amp
is best.

Is This Answer Correct ?    50 Yes 35 No

how to calculate cable size, olr rating, contactor rating and mccb rating,to below given details t..

Answer / pvr.parthasarathi

75 Kw motor takes 134 amps full load current. But for
selecting its Cable, Contactor, OLR and MCCB, we have to
consider many other factors such as need of its operation.
Place of the Motor Control Centre and possibility of laying
the cable Wheter inside the duct, underground or in the
air. For selection of the Contactor enclosure of the
panel, its environments etc are to be taken into
consideration. So giving answer at a stretch basing on
some thumb rule is not technically qualified.

Other particulars are required.

Is This Answer Correct ?    19 Yes 5 No

how to calculate cable size, olr rating, contactor rating and mccb rating,to below given details t..

Answer / v.raguvaran

THE MOTOR AMP IS 130AMP.THE CABLE(USE COPPER ) SIZE SHOULD BE 45sq.mm (delta connection),35sq.mm(star delta)
OLR RATING IS (125-135) BUT STANDARD SIZE IS (130-175)ABB
CONTACTOR RATING IS 200A(DELTA),100(MAIN)-100(DELTA)-50(STAR)
MCCB RATING IS 250A

Is This Answer Correct ?    0 Yes 0 No

how to calculate cable size, olr rating, contactor rating and mccb rating,to below given details t..

Answer / mohamed-mohamed

i know> but my nglish not well> because of that i can not answer

Is This Answer Correct ?    1 Yes 4 No

how to calculate cable size, olr rating, contactor rating and mccb rating,to below given details t..

Answer / rsbangra

motor rating 75kw,so it taken full load p=1.732*v*I*cosfy
i= p/1.732*v*cosfy
=123 amp. so we requared a cable to carry 123 amp
contonious rating. so require to run motor in star delta
starter . in star delta connection load current is 58% of
line current. we require 58% of 123 amp carring capasity
cable.it is around 71 amp.generly copper cable taking 4
times current of cable rating and alluminium cable taken
1.5 times of cable ratting .so for 71 amp carring alu.
cable 50mm2 suffisent but due to high starting curent its
take 70 mm2 cable ib best.
its overload relay ratting is in range to 71 amp. it to be
60-80 amp,and mccb rating is 2.5 times of full load =300amp
is best.

Is This Answer Correct ?    47 Yes 57 No

Post New Answer

More Electrical Engineering Interview Questions

Witch do depand of Power factor and theory of power factor?

0 Answers  


Why earthing is necessary for any equipment?

0 Answers  


4-Why we measure the insulation resistance of main core and frame in spite of that must be connected with ground before energize the transformer?

3 Answers  


what is balanced network and unbalanced network

1 Answers   Nalco,


What is the main cause of magnetism?

0 Answers  


what is R Core Transformer. how it differs from normal transformers. dont search in net and post the answer.

0 Answers  


Is it possible to use a S1 duty class motor for crane application (S4)? If not, why?

0 Answers  


At which time Synchronous generator act as a Synchronous Condenser?

1 Answers  


When we need up only in o/p 440v, so why we use directly in 11kva in input?

0 Answers   Lupin, Medhaj Techno Concept,


Why are calling lagging power factor is a inductive load?

2 Answers  


What is TR of AC?

11 Answers   Carrier, Reliance,


What will be advantage if we put some load in neutral of grounded star transformer & loadshortcircuit current,rated current of cable & MCB with example?

0 Answers  


Categories
  • Civil Engineering Interview Questions Civil Engineering (5086)
  • Mechanical Engineering Interview Questions Mechanical Engineering (4456)
  • Electrical Engineering Interview Questions Electrical Engineering (16639)
  • Electronics Communications Interview Questions Electronics Communications (3918)
  • Chemical Engineering Interview Questions Chemical Engineering (1095)
  • Aeronautical Engineering Interview Questions Aeronautical Engineering (239)
  • Bio Engineering Interview Questions Bio Engineering (96)
  • Metallurgy Interview Questions Metallurgy (361)
  • Industrial Engineering Interview Questions Industrial Engineering (259)
  • Instrumentation Interview Questions Instrumentation (3014)
  • Automobile Engineering Interview Questions Automobile Engineering (332)
  • Mechatronics Engineering Interview Questions Mechatronics Engineering (97)
  • Marine Engineering Interview Questions Marine Engineering (124)
  • Power Plant Engineering Interview Questions Power Plant Engineering (172)
  • Textile Engineering Interview Questions Textile Engineering (575)
  • Production Engineering Interview Questions Production Engineering (25)
  • Satellite Systems Engineering Interview Questions Satellite Systems Engineering (106)
  • Engineering AllOther Interview Questions Engineering AllOther (1379)