Answer / devendra_kushwaha27
A process used to determine the differential pressure
present within a liquid-filled space.
The formula for determining the differential pressure
within a wet leg design is: d/p = h (SG)
Where: d/p = differential pressure, h = height of liquid
present, and SG = specific gravity
When the process vapors condense at normal ambient
temperatures or are corrosive, this reference leg can be
filled to form a wet leg. If the process condensate is
corrosive, unstable, or undesirable to use to fill the wet
leg, this reference leg can be filled with an inert liquid.
| Is This Answer Correct ? | 18 Yes | 0 No |
how to work MIL contol valve posistioner ?
How can we say that accuracy of measurement increases by using 3 or 4 wire RTD? because for example: If resistance of RTD element is say r ohms and Resistance of the cable from transmitter to RTD is R ohms And if 4 wire RTD is used, ____._____________________ R ohms | |_____._____________________ R ohms / \ / r ohms \ \ | |______.__________________ R Ohms | |_______._________________ R ohms Then the actual resistance measured will be: Total = r + R/2 + R/2 = r +R Ohms Note: r+R instead of r ohms. hence error
How comparison of objects is done in PHP5?
Hello-I know this not an engineering question,I am working in gulf & i want to do correspondence diploma in instrumentation,can any one give me the address of any university in which this courses are available.
What is force balance principle?
I have a MRE200 amplifier for controlling a mitsubishi servo motor, I would like to know how many pulses are required to rotate the servo motor by 1 degree and what must be the pulse width
what is difference between 3 wire and 4 wire RTD sensor?
12 Answers HTA Instrumentation,
We do have a problem in the company that is one PT connected to PlC which is mean 1 out of 1 in PLC system we do have the PAHH is 55 mbar and PALL 8 mbar with a timer of 15 sec for the PAHH the problem started when PAHH goes more than the set point which is 55 it reached up to 71 but due to timer doesn't trip . We force it and we checked everything nothing there . We replaced the transmitter problem still there the reading goes more than the 55 bar the range for transmitte is 0- 60 mbar . So we did loop check , aculaizing valve , wiring all are okay . What the possible causes for this ???
2 Answers National Petrochemical Company,
What are the key components of control loop?
Hi friends, from Aug 4th onwards iam getting spikes for analog inputs in our DCS for a period of 800ms. I throughly checked every thing, finally i found that the DI, DO's from MCC panels shields are terminated in the Signal Earth where Analog Input signals shields are terminated. Is there any problem with this type of termination?. i checked the induction voltage from MCC and getting around 25VAC, please suggest me in this concern. Our plant is 8months old only. DCS is Siemens Make Simatic PCS7, and the transmitters are Yokogawa make.
please tell me how to convert double acting ytc positioner yt-1200 into single acting ytc positioner ?
why we are using -24 vdc in plc?
Civil Engineering (5086)
Mechanical Engineering (4453)
Electrical Engineering (16638)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)