what is the meaning of wet leg & where is it used?



what is the meaning of wet leg & where is it used?..

Answer / devendra_kushwaha27

A process used to determine the differential pressure
present within a liquid-filled space.

The formula for determining the differential pressure
within a wet leg design is: d/p = h (SG)

Where: d/p = differential pressure, h = height of liquid
present, and SG = specific gravity

When the process vapors condense at normal ambient
temperatures or are corrosive, this reference leg can be
filled to form a wet leg. If the process condensate is
corrosive, unstable, or undesirable to use to fill the wet
leg, this reference leg can be filled with an inert liquid.

Is This Answer Correct ?    18 Yes 0 No

Post New Answer

More Instrumentation Interview Questions

how to work MIL contol valve posistioner ?

1 Answers   ABB,


How can we say that accuracy of measurement increases by using 3 or 4 wire RTD? because for example: If resistance of RTD element is say r ohms and Resistance of the cable from transmitter to RTD is R ohms And if 4 wire RTD is used, ____._____________________ R ohms | |_____._____________________ R ohms / \ / r ohms \ \ | |______.__________________ R Ohms | |_______._________________ R ohms Then the actual resistance measured will be: Total = r + R/2 + R/2 = r +R Ohms Note: r+R instead of r ohms. hence error

2 Answers  


How comparison of objects is done in PHP5?

1 Answers   TIS,


Hello-I know this not an engineering question,I am working in gulf & i want to do correspondence diploma in instrumentation,can any one give me the address of any university in which this courses are available.

2 Answers  


What is force balance principle?

1 Answers  


I have a MRE200 amplifier for controlling a mitsubishi servo motor, I would like to know how many pulses are required to rotate the servo motor by 1 degree and what must be the pulse width

1 Answers   Essar,


what is difference between 3 wire and 4 wire RTD sensor?

12 Answers   HTA Instrumentation,


We do have a problem in the company that is one PT connected to PlC which is mean 1 out of 1 in PLC system we do have the PAHH is 55 mbar and PALL 8 mbar with a timer of 15 sec for the PAHH the problem started when PAHH goes more than the set point which is 55 it reached up to 71 but due to timer doesn't trip . We force it and we checked everything nothing there . We replaced the transmitter problem still there the reading goes more than the 55 bar the range for transmitte is 0- 60 mbar . So we did loop check , aculaizing valve , wiring all are okay . What the possible causes for this ???

2 Answers   National Petrochemical Company,


What are the key components of control loop?

1 Answers  


Hi friends, from Aug 4th onwards iam getting spikes for analog inputs in our DCS for a period of 800ms. I throughly checked every thing, finally i found that the DI, DO's from MCC panels shields are terminated in the Signal Earth where Analog Input signals shields are terminated. Is there any problem with this type of termination?. i checked the induction voltage from MCC and getting around 25VAC, please suggest me in this concern. Our plant is 8months old only. DCS is Siemens Make Simatic PCS7, and the transmitters are Yokogawa make.

1 Answers  


please tell me how to convert double acting ytc positioner yt-1200 into single acting ytc positioner ?

1 Answers  


why we are using -24 vdc in plc?

1 Answers   CGL,


Categories
  • Civil Engineering Interview Questions Civil Engineering (5086)
  • Mechanical Engineering Interview Questions Mechanical Engineering (4453)
  • Electrical Engineering Interview Questions Electrical Engineering (16638)
  • Electronics Communications Interview Questions Electronics Communications (3918)
  • Chemical Engineering Interview Questions Chemical Engineering (1095)
  • Aeronautical Engineering Interview Questions Aeronautical Engineering (239)
  • Bio Engineering Interview Questions Bio Engineering (96)
  • Metallurgy Interview Questions Metallurgy (361)
  • Industrial Engineering Interview Questions Industrial Engineering (259)
  • Instrumentation Interview Questions Instrumentation (3014)
  • Automobile Engineering Interview Questions Automobile Engineering (332)
  • Mechatronics Engineering Interview Questions Mechatronics Engineering (97)
  • Marine Engineering Interview Questions Marine Engineering (124)
  • Power Plant Engineering Interview Questions Power Plant Engineering (172)
  • Textile Engineering Interview Questions Textile Engineering (575)
  • Production Engineering Interview Questions Production Engineering (25)
  • Satellite Systems Engineering Interview Questions Satellite Systems Engineering (106)
  • Engineering AllOther Interview Questions Engineering AllOther (1379)