What is the formula to find out the kvar required to
improve the powerfactor from .85 to .99 at 1500kw, 415v.
Answers were Sorted based on User's Feedback
The KVAR required is:
KVAR=KW(tan@1-tan@2) (where @1=cos-1(p.f1)& @2=cos-1(p.f2)
Therefore,
KVAR=KW {tan[cos-1(p.f1)]-tan[cos-1(p.f2)]}
=KW {tan[cos-1(0.85)]-tan[cos-1(0.99)]}
=KW {tan[31.79]-tan[8.11]}
=KW {0.48}
=1500 {0.48}
=720
Therefore 720 KVAR is required to improve powerfactor from
0.85 to 0.99 for 1500KW load.
NOTE:-
Excuse me if the answer is wrong.
| Is This Answer Correct ? | 14 Yes | 2 No |
Answer / alimohmad khatri
KVAR=KVA*SIN(PHI)
KW=KVA*COS(PHI)
HENCE....KVAR/KW=TAN(PHI)
KVAR=KW*TAN(PHI)
NOW, FOR P.F.(1)=COS(PHI(1))=.85 THEN TAN(PHI(1))=.6197
FOR P.F.(2)=COS(PHI(2))=.99 THEN TAN(PHI(2))=.1425
KW=1500 KW IS COMMON FOR BOTH CASE 1 & 2
REQUIRED....
KVAR=KW*[TAN{PHI(1)}-TAN{PHI(2)}]
HENCE KVAR=1500*(0.6197-0.1425)=715.8
YOU NEED TO ARRANGE CAPACITOR BANK OF 715.8 KVAR.
| Is This Answer Correct ? | 6 Yes | 0 No |
Answer / waqi
first calculate the kva at .99 and 1500kw
(cosp=kw/kva),than put the value of kva in this formula kva=
(kw)2+(kvar)2)^1/2 to caculate kvar at .99 pwr factor
| Is This Answer Correct ? | 0 Yes | 0 No |
Answer / habeebm
Dear Waqi
I am not understand your answer for the above mentioned question. Will you please solve and give us the answer for required KVAR to improve power factor from 0.85 to 0.99 for 1500KW load.
| Is This Answer Correct ? | 0 Yes | 1 No |
What should be current in the Primary and secondary side of 1000KVA (11KV Supply)Transformer.?
what is a speed of rotor when we give supply to stator of 50hz and as well as rotor of 60hz of an induction motor?????
why dont we use the same pylon to carry 400 kv plus 220kv and 33 kv ?
2 Answers Focus, Focus Energy,
What is d main advantage of using double circuit 3 phase transmission ?
What is vaccum currcuit breaker.define with cause and where be use it device?
what r substations?what r there work?why voltages r incresed and then reduced during distribution of power
Why the core in the distribution transformer is in even number
how to apply b license to c license in tneb
PLZ sent the previous year question paper for GET in NHPC on my EMail id ppshanker@gmail.com
what methods are used to improve power factor?
transformer 3 ph, 225 kva pri 480v, sec 208v. primary neutral connected to system, is secondary neutral to be grounded and how
Define active and passive network?
Civil Engineering (5086)
Mechanical Engineering (4453)
Electrical Engineering (16638)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)