What is the formula to find out the kvar required to
improve the powerfactor from .85 to .99 at 1500kw, 415v.
Answers were Sorted based on User's Feedback
The KVAR required is:
KVAR=KW(tan@1-tan@2) (where @1=cos-1(p.f1)& @2=cos-1(p.f2)
Therefore,
KVAR=KW {tan[cos-1(p.f1)]-tan[cos-1(p.f2)]}
=KW {tan[cos-1(0.85)]-tan[cos-1(0.99)]}
=KW {tan[31.79]-tan[8.11]}
=KW {0.48}
=1500 {0.48}
=720
Therefore 720 KVAR is required to improve powerfactor from
0.85 to 0.99 for 1500KW load.
NOTE:-
Excuse me if the answer is wrong.
| Is This Answer Correct ? | 14 Yes | 2 No |
Answer / alimohmad khatri
KVAR=KVA*SIN(PHI)
KW=KVA*COS(PHI)
HENCE....KVAR/KW=TAN(PHI)
KVAR=KW*TAN(PHI)
NOW, FOR P.F.(1)=COS(PHI(1))=.85 THEN TAN(PHI(1))=.6197
FOR P.F.(2)=COS(PHI(2))=.99 THEN TAN(PHI(2))=.1425
KW=1500 KW IS COMMON FOR BOTH CASE 1 & 2
REQUIRED....
KVAR=KW*[TAN{PHI(1)}-TAN{PHI(2)}]
HENCE KVAR=1500*(0.6197-0.1425)=715.8
YOU NEED TO ARRANGE CAPACITOR BANK OF 715.8 KVAR.
| Is This Answer Correct ? | 6 Yes | 0 No |
Answer / waqi
first calculate the kva at .99 and 1500kw
(cosp=kw/kva),than put the value of kva in this formula kva=
(kw)2+(kvar)2)^1/2 to caculate kvar at .99 pwr factor
| Is This Answer Correct ? | 0 Yes | 0 No |
Answer / habeebm
Dear Waqi
I am not understand your answer for the above mentioned question. Will you please solve and give us the answer for required KVAR to improve power factor from 0.85 to 0.99 for 1500KW load.
| Is This Answer Correct ? | 0 Yes | 1 No |
how to test generator protection rotor earth fault relay and locked rotor test?
how do i calculate voltage drop-if length is 1000 meter,amps is 160a
Why DC current is not used in transformer?
What is the unit of vaccum?
difference between over current and over load protection?
What is time invariant system?
In star delta Schematic can we connect OLR in delta circuit
How can we connect additional batteries to three phase ups? What are parameters we have to check when connecting?
I am an American living in Vietnam and I have recently gotten a refrigerator from Japan and it is rated for 100 vac, but the power here is 220 so I bought a voltage stabilizer it has a 1 kva output rating. Can you please tell me what the amperage is? I'm confused and without a working fridge.
you have a 2 tonne ac that operates for 2 hrs daily what will be you monthly bill (this is complete question asked nothing else was given)?
How is earthing done in Aerospace applications such as Flights and spaceships..?
Why the Transformer Nuetral is grounded?
10 Answers Infosys, Khartoum Refinery,
Civil Engineering (5086)
Mechanical Engineering (4456)
Electrical Engineering (16639)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)