What is the formula to find out the kvar required to
improve the powerfactor from .85 to .99 at 1500kw, 415v.
Answers were Sorted based on User's Feedback
The KVAR required is:
KVAR=KW(tan@1-tan@2) (where @1=cos-1(p.f1)& @2=cos-1(p.f2)
Therefore,
KVAR=KW {tan[cos-1(p.f1)]-tan[cos-1(p.f2)]}
=KW {tan[cos-1(0.85)]-tan[cos-1(0.99)]}
=KW {tan[31.79]-tan[8.11]}
=KW {0.48}
=1500 {0.48}
=720
Therefore 720 KVAR is required to improve powerfactor from
0.85 to 0.99 for 1500KW load.
NOTE:-
Excuse me if the answer is wrong.
Is This Answer Correct ? | 14 Yes | 2 No |
Answer / alimohmad khatri
KVAR=KVA*SIN(PHI)
KW=KVA*COS(PHI)
HENCE....KVAR/KW=TAN(PHI)
KVAR=KW*TAN(PHI)
NOW, FOR P.F.(1)=COS(PHI(1))=.85 THEN TAN(PHI(1))=.6197
FOR P.F.(2)=COS(PHI(2))=.99 THEN TAN(PHI(2))=.1425
KW=1500 KW IS COMMON FOR BOTH CASE 1 & 2
REQUIRED....
KVAR=KW*[TAN{PHI(1)}-TAN{PHI(2)}]
HENCE KVAR=1500*(0.6197-0.1425)=715.8
YOU NEED TO ARRANGE CAPACITOR BANK OF 715.8 KVAR.
Is This Answer Correct ? | 6 Yes | 0 No |
Answer / waqi
first calculate the kva at .99 and 1500kw
(cosp=kw/kva),than put the value of kva in this formula kva=
(kw)2+(kvar)2)^1/2 to caculate kvar at .99 pwr factor
Is This Answer Correct ? | 0 Yes | 0 No |
Answer / habeebm
Dear Waqi
I am not understand your answer for the above mentioned question. Will you please solve and give us the answer for required KVAR to improve power factor from 0.85 to 0.99 for 1500KW load.
Is This Answer Correct ? | 0 Yes | 1 No |
condider as 100 w lamps glowing . for completing a one unit how much time it should glow
We have given to 3phase supply to ups system & how can coming netural
i am confused about generator. i have generator of 380 KVA that is 304 KW by that formula KW=KVA*0.8... then by this formula I=KW/V*1.732*0.8 the amperes are 528.673. so that is the load which i put on one phase of generator or this is total 3 phase load on Generator.......
why the India electrical supply transmission loss is high when compare to us
What is lifting power for 1 wb/m2 and 1 A magnet?
WHY IS wet surface used for grounding???
How do we measure earth fault current in Generator Transformer(20/420kv),Station Transformer(20/11 kv) and Unit Transformers(20/11kv) for our plant system, since these don't have any Neutral earth Fault relay connected to their Neutral Earth? But for Unit Service transformers(11/.433 Kv) we have an Earth Fault Relay connected to its neutral earth.Why is such so?
What is the difference when selecting a cable between AC and DC current?
what's burden resistor, why it's used?
what are the main parts of DG? explian thier functions?
8 Answers Apollo Power, Tata DoCoMo, Tyco, Vizag Steel,
why the neutral line is not giving shock to us if we touch it ?
Can i use the B-curve MCB instead of C-curve MCB