why single phase induction motors are not self staring ?
how can we start the 1-phase Induction motor ?
Answers were Sorted based on User's Feedback
Answer / ajith
the 1ph supply applied to stator wdng cant produce a
rotating magnetic field as in the case of a 3ph induction
motor..
if a 1ph is applied to the induction motor the resulting
magnetic field is only altrnating (not rotating)..
In order to make the 1ph induction motor self starting...,
2 windings are used ..startin windin n runnin wdng..called
split phase motor.. or by connectin a capacitor in series
with the start wdng.. for obtainin necessary phase
diplacement...
| Is This Answer Correct ? | 38 Yes | 2 No |
Answer / abhimanyu kumar gupta
Single phase IM given single phase supply given to stator
winding an alternating magnetic field develop in stator and
produce alternating flux and collides with rotor winding and
produce induced EMF at rotor since the rotor winding are
closed this produce induced current in rotor.
Due to this induced current in magnetic field of alternating
nature and this nature is not rotating. Both magnetic field
in stator and rotor are Colline's so resultant torque rotor
will 0. Hence single phase IM does not self start.
In order to make motor self start an external force to the
rotor should be given because of locking of field will
disappear.
| Is This Answer Correct ? | 3 Yes | 2 No |
An input device is interfaced with Intel 8085A microprocessor as memory mapped I/O.The address of the device is 2500H.In order to input data from the device to accumulator,the sequence of instruction will be
why neutral should connect to earth in delta-star type transformer
Why the capacitor are connected in Delta(Three Phase) for power factor improvement ?
which type your UPS on line,off line give the reason?
what is the power factor of an inductive load ? (i) Zero (ii) Lagging (iii) Leading (iv) Unity
how capacitor pass ac voltage practically?with increase frequency and cpacitance?
what is mean by drives?
why we use to always generate power below 16kv.why not at higher voltage?
I have a relay contact rated at 220v dc which is supplied with a 24vdc from the panel,for it to trip the dampers(24vdc).What if the application of the relay changes so that it should work at its rated 220vdc then will it work at 24vdc supply given or any other consideration needs to be taken .....
what is meaning of AMF, WHY IS USING IN GENSET
A 11KV, 1200 A breaker combination fixed in a cubicle for HT motor.Is normally for 11 KV motor fuse is using? if Yes, What range fuse is required?
what is the formula to find Amp. for an 3 phase moter both if H.P. or if kW is known?
Civil Engineering (5086)
Mechanical Engineering (4456)
Electrical Engineering (16639)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)