Golgappa.net | Golgappa.org | BagIndia.net | BodyIndia.Com | CabIndia.net | CarsBikes.net | CarsBikes.org | CashIndia.net | ConsumerIndia.net | CookingIndia.net | DataIndia.net | DealIndia.net | EmailIndia.net | FirstTablet.com | FirstTourist.com | ForsaleIndia.net | IndiaBody.Com | IndiaCab.net | IndiaCash.net | IndiaModel.net | KidForum.net | OfficeIndia.net | PaysIndia.com | RestaurantIndia.net | RestaurantsIndia.net | SaleForum.net | SellForum.net | SoldIndia.com | StarIndia.net | TomatoCab.com | TomatoCabs.com | TownIndia.com
Interested to Buy Any Domain ? << Click Here >> for more details...


Can we use 11kv Trivector Metre or Energy metre instead
33kv Metre at 33kv Over Head Line metering purpose?

Answers were Sorted based on User's Feedback



Can we use 11kv Trivector Metre or Energy metre instead 33kv Metre at 33kv Over Head Line metering..

Answer / k.prakashchandra

The voltage input to almost all energy meters is 110 V line
to line ,which is the secondary voltage of PTs. You can use
them for all system voltages by applying the correct MF .

Is This Answer Correct ?    4 Yes 1 No

Can we use 11kv Trivector Metre or Energy metre instead 33kv Metre at 33kv Over Head Line metering..

Answer / mu

we can use any meter at this point as we have to only
change CT & PT's before commissioning,
I have used 11kv meter in 33 kv installation with similar
changes, usual practice done by SEB's across india when
supply voltage changes for any project.

Is This Answer Correct ?    3 Yes 1 No

Can we use 11kv Trivector Metre or Energy metre instead 33kv Metre at 33kv Over Head Line metering..

Answer / vimal patel

All digital meters can be used at any place like 220kv,66 kv , 33 kv and also 11kv..but first u have to see that metering range of Voltage and Current so u have to adjust that all phase Ct and PT Ratio upto that meter range and than find that MF ( Multiplying factor ) to get Unit.

Is This Answer Correct ?    2 Yes 1 No

Can we use 11kv Trivector Metre or Energy metre instead 33kv Metre at 33kv Over Head Line metering..

Answer / k.prakashchandra

The voltage input to both the meters is 110 V.So, you can
use and pre-set meter constant is to be considered

Is This Answer Correct ?    2 Yes 1 No

Can we use 11kv Trivector Metre or Energy metre instead 33kv Metre at 33kv Over Head Line metering..

Answer / saleem

The Digital Meter can be used with proper setting, however
the analog meter can not be used because its dial is
calibrated for 11KV.

Is This Answer Correct ?    3 Yes 4 No

Post New Answer

More Electrical Engineering Interview Questions

is there any difference between inverter and a battery

2 Answers   Cummins,


Dear sir, In our plant have Station Transformer having capacity,i want to know, why LV side 40 - 40MVA is given? & how we can get 6.3 KV supply from tertiary(i.e. Open delta connection), Vector Group YNyn0 - yn0 +d MVA Rating 80MVA / 40 - 40MVA + 26.7MVA Voltage rating 420 (Tap range +6,to -10)81.25% /11.5KV - 11.5KV +6.3KV

0 Answers   Bhel,


what is JE exam?

0 Answers  


I If i have 2kv ups in which 38Amp *8battries hou many hour's back up i get from 600Watts

2 Answers  


What is an infinite bus bar?

34 Answers  


We have 2 no. 4MW DG set. and GEB supply. But, we running, only 1 DG set. when we done APFC/Power factor setting : 0.90, then winding temp. Low. but when setting done : 0.83, then Winding temp. increase. WHY Why ? ? ?, plz give me answer.

4 Answers  


What are the precautions to be taken before working on a cable?

1 Answers   Alfanar,


Will The Rated Capacity of 20 MVA ,220/6.6 KV, ONAN cooling Power Tranformer be increased up to 25 MVA with respect to its %Impedence by ONAF cooling with same rating..?

2 Answers   Ambuja,


What is maximum AC & DC transmission voltage in India? and where?

12 Answers  


what is the right cable size for 100 hp mpter.

3 Answers  


what is the grounding Calculation formula? spouse i want to provide grounding to 3phase 18kw motor or i want to provide ground to 3phase 10kva dry type transformere or you give me any exemple...... Thanks.

0 Answers  


Two electrically operated Vibro Motors are fixed in parallel direction in vibrating feeder. What is the direction of both Vibro Motors?

1 Answers  


Categories
  • Civil Engineering Interview Questions Civil Engineering (5086)
  • Mechanical Engineering Interview Questions Mechanical Engineering (4456)
  • Electrical Engineering Interview Questions Electrical Engineering (16639)
  • Electronics Communications Interview Questions Electronics Communications (3918)
  • Chemical Engineering Interview Questions Chemical Engineering (1095)
  • Aeronautical Engineering Interview Questions Aeronautical Engineering (239)
  • Bio Engineering Interview Questions Bio Engineering (96)
  • Metallurgy Interview Questions Metallurgy (361)
  • Industrial Engineering Interview Questions Industrial Engineering (259)
  • Instrumentation Interview Questions Instrumentation (3014)
  • Automobile Engineering Interview Questions Automobile Engineering (332)
  • Mechatronics Engineering Interview Questions Mechatronics Engineering (97)
  • Marine Engineering Interview Questions Marine Engineering (124)
  • Power Plant Engineering Interview Questions Power Plant Engineering (172)
  • Textile Engineering Interview Questions Textile Engineering (575)
  • Production Engineering Interview Questions Production Engineering (25)
  • Satellite Systems Engineering Interview Questions Satellite Systems Engineering (106)
  • Engineering AllOther Interview Questions Engineering AllOther (1379)