Can we use 11kv Trivector Metre or Energy metre instead
33kv Metre at 33kv Over Head Line metering purpose?
Answers were Sorted based on User's Feedback
Answer / k.prakashchandra
The voltage input to almost all energy meters is 110 V line
to line ,which is the secondary voltage of PTs. You can use
them for all system voltages by applying the correct MF .
| Is This Answer Correct ? | 4 Yes | 1 No |
Answer / mu
we can use any meter at this point as we have to only
change CT & PT's before commissioning,
I have used 11kv meter in 33 kv installation with similar
changes, usual practice done by SEB's across india when
supply voltage changes for any project.
| Is This Answer Correct ? | 3 Yes | 1 No |
Answer / vimal patel
All digital meters can be used at any place like 220kv,66 kv , 33 kv and also 11kv..but first u have to see that metering range of Voltage and Current so u have to adjust that all phase Ct and PT Ratio upto that meter range and than find that MF ( Multiplying factor ) to get Unit.
| Is This Answer Correct ? | 2 Yes | 1 No |
The voltage input to both the meters is 110 V.So, you can
use and pre-set meter constant is to be considered
| Is This Answer Correct ? | 2 Yes | 1 No |
Answer / saleem
The Digital Meter can be used with proper setting, however
the analog meter can not be used because its dial is
calibrated for 11KV.
| Is This Answer Correct ? | 3 Yes | 4 No |
is there any difference between inverter and a battery
Dear sir, In our plant have Station Transformer having capacity,i want to know, why LV side 40 - 40MVA is given? & how we can get 6.3 KV supply from tertiary(i.e. Open delta connection), Vector Group YNyn0 - yn0 +d MVA Rating 80MVA / 40 - 40MVA + 26.7MVA Voltage rating 420 (Tap range +6,to -10)81.25% /11.5KV - 11.5KV +6.3KV
what is JE exam?
I If i have 2kv ups in which 38Amp *8battries hou many hour's back up i get from 600Watts
What is an infinite bus bar?
We have 2 no. 4MW DG set. and GEB supply. But, we running, only 1 DG set. when we done APFC/Power factor setting : 0.90, then winding temp. Low. but when setting done : 0.83, then Winding temp. increase. WHY Why ? ? ?, plz give me answer.
What are the precautions to be taken before working on a cable?
Will The Rated Capacity of 20 MVA ,220/6.6 KV, ONAN cooling Power Tranformer be increased up to 25 MVA with respect to its %Impedence by ONAF cooling with same rating..?
What is maximum AC & DC transmission voltage in India? and where?
what is the right cable size for 100 hp mpter.
what is the grounding Calculation formula? spouse i want to provide grounding to 3phase 18kw motor or i want to provide ground to 3phase 10kva dry type transformere or you give me any exemple...... Thanks.
Two electrically operated Vibro Motors are fixed in parallel direction in vibrating feeder. What is the direction of both Vibro Motors?
Civil Engineering (5086)
Mechanical Engineering (4456)
Electrical Engineering (16639)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)