shall we use a machine having 60Hz frequency in india ? why?
Answers were Sorted based on User's Feedback
Answer / asif.k64@hotmail.com
In India, Electrical power is generated at 50Hz, unlike UK
US and other western countries.
A 60Hz motor should not be used as it may get damaged.
However you can use it with the help of a VFD (variable
frequency drive)
| Is This Answer Correct ? | 6 Yes | 0 No |
in addition to #1 answer, if you're using 60Hz motor on 50Hz, the speed will be rated based on 50Hz and you may loose the designed torque hence require more current to run
| Is This Answer Correct ? | 4 Yes | 0 No |
Answer / gaurav tripathi
we can use machine on 60 hz by using cycloconverter and
filters
| Is This Answer Correct ? | 3 Yes | 0 No |
Answer / raghu
i think the resistance and reactance of that machine will vary also thickness of lamination sheets of that machine are designed for that frequency only(60).
| Is This Answer Correct ? | 0 Yes | 0 No |
what is the difference between torque induced and torque load?compare them with respect to dc motor?
what is upper impedance and lower impedance of a distance relay
how can we select the rating of Load break switch that is connected to the primary protection of 200 kva 11kv/415v distribution transformer?? step by step calculated answr pls...thnk.u
What is Isolation Current transformer and what purpose to use it in REF relay ?
Practical condition in 400KV Sub station:- Breaker(open) , isolator(open), Earthing (close) at both end e.g A & B. Now Open A Stn Earthing than Open B stn Earthing (Which have a 50MVA reactor) , AND suddenly show R,Y,B phase 704KV,573KV,118KV respectively. Que is without closing of breaker how it is possible.???? My Whats app No:07621840498 for Further Discussion. Pls experts suggest.
Is it any dc fuses availbale in market? can we use one fuse for both AC & DC ?
What is difinition of HIGH RESISTANCE FAULT and LOW RESISTANCE FAULT?
please send me jindal previous aptitude and technical question and answer.my email id is deep_raj@live.com
A motor works on 30kw.it is working on 440volts.How much amper will be Required?
what is cogging and crawling
we have a 2000kva step down transformer at our site. The HT side is charged from 22000V. So the primary current will be 52.48A. So why the HT breaker(SF6 ABB) is rated of 1250Amps ?
with help of neat sketch explain principle of TIG welding process
Civil Engineering (5086)
Mechanical Engineering (4456)
Electrical Engineering (16639)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)