how to install Differential pressure transmitter in gas
line.i need transmitter down side.
Answers were Sorted based on User's Feedback
Answer / www.islamqa.com
Bharathi is right, we have to use "condensation pot"
# Actually the gas is "self venting" and the instrument
mounting should be above the pipeline in order to avoid
vapor condensation which cuase fault reading.
# For liquid service the instrument mounting should be
below the pipeline as the liquid is "self draining".
# If we want to mount the instrument below the pipeline in
gas service we should use "condensation pot" and the
operator should drain it regularly to avoid fault reading.
# In steam service we use the condensation pot also and it
should be fully filled with water and its mounting should
be in the same pipeline level and the instrument itself
will be below the pipeline, this link indicte the situation:
http://www.eng-tips.com/viewthread.cfm?qid=166893&page=97
the aim of water filling is to provide a solid motion
transfer in order to have a good accuracy.
Regards,
Ahmed Sabry
Control and Instrumentation Engineer
GPC - General Petroleum Company
CELL.: 00 2 0121367310
Is This Answer Correct ? | 14 Yes | 1 No |
Answer / ravi
you can use the txe down, which measures level or flow, we
have to make impulse line downwards by taking flange
opening at the top of process line. we have to give steam
line over the entire impulse line, so that gas especially
LPG will not condense at atmospherice temp, and it will
give the correct pressure across the diaphram of DP, so
that correct level can be mearure.
Is This Answer Correct ? | 13 Yes | 2 No |
Answer / hemant bhati
You can bring the Transmitter down side only when you
provide a diagram seal type of arrangement even there is
gas line.
Is This Answer Correct ? | 10 Yes | 3 No |
Answer / snehal
place the taps side of the line
place the transmitter beside/above the line so that
condensed fluid will drain off
Is This Answer Correct ? | 3 Yes | 0 No |
Answer / kk
transmitter taps should be greater than 45 from both taps
Is This Answer Correct ? | 1 Yes | 1 No |
Answer / krishna
YOU CAN INSTALL TRANSMITTER DOWN SIDE SO THAT YOU SHOULD
MAKE IMPULSE LINES ACCORDING TO REQUIREMENT . TRANSMITTER
RANGE WILL CHANGE ACCORDING TO DISTANCE FROM TANK TO THE TX
LEVEL .OTHERWISE ERROR WILL ERAISE
Is This Answer Correct ? | 5 Yes | 6 No |
Answer / bharathi
You can bring the impulse line as you want. But the only
thing is u should provide condensate pot at drain point. al
so provide steam trace over the impulse line. It will
avoided rate of condensate. If you install without this
condensate pot the transmitter reading starts fluctuate
frequently.
Is This Answer Correct ? | 2 Yes | 3 No |
what is meant by control valve sizing?
There are many type of control cable like pair,core,tried, What are defination each one
In control engg. : Differences b/w 1st order & 2nd order system, graphically & theoretically ?
how do we commission inergen system?
diff c and c++
What is DeltaV?
What is difference between “Fault Tolerant” & “Fault avoidance” PLC? Application where these system s are used?
Explain how thw analog to digital converter works with the circuit diagram
Who to difference between analog in & analog out in dcs?
how does we calibrate a square root flow transmitter ,give an example and explain it step by step like range calculation , calibration hook up series connection , zero check , and how to apply pressure , and if not geting proportional output then what should we do ?
What are the types of control valves available
I need the intools training institute address in india. Intools subject oriented local authors books.Refer me plz