If a 3 phase transformer is a 500 kva using the formulae
500kva= 500000/433 x 1.732 = 666.71amps does this mean that
each phase on the secondary side is 666.71
Answers were Sorted based on User's Feedback
Answer / k.prakashchandra
The VA per phase is (500/3 KVA) 166.67 x 1000 , phase
voltage is(433/1.732) 250 V.Then current in each phase is
166670/250= 666.68 A
Is This Answer Correct ? | 8 Yes | 4 No |
Answer / shyam
The value 666.71 A gives the current rating i.e the maximum
current that the transformer secondary winding (each phase)
can withstand.The operating value may be less than or equal
to this RATING...
Is This Answer Correct ? | 0 Yes | 0 No |
Answer / lalit pratap
Yes It's caring 666.71amps on each phase on secondary winding in transformer.
Is This Answer Correct ? | 0 Yes | 2 No |
what is the responsibilities of electrical project engineer?
in our sub station why we step down firstly 33kv\11kv then 11kv to 430v. can we direct step down 33v to 430.v.
1.Why hydrogen used for cooling in generators 2.Why electrical equipment protected by ground 3.Why earthing for transmission line 4.What is rms value of half wave rectified square wave. If Rms value of actual wave 2amps.
what is first pole to clear factor ?
A parallel flow heat exchanger will perform better than a counter flow heat exchanger. State if the statement is true or false.
I have a situation to design sub-Distribution board/Panel meant for feeding power sockets. In the incomer CAN i Take TP MCCB with Neutral Link and All the outgoing feeders with to sockets with TP MCCB and Neutral Link? P.S : My System is IT Earthing
what is interpose vt where it is used and y it is used?
explain transformer ct connection?
what is reasion of harmonic create the power supply , And how to reduced to harmonic
what is the difference between on line UPS & INVERTOR
As all us know that the capacitor panel is connected to improve the power factor when it is PF is low. whether we can connect the capacitor panel on D.G. side(? If it is yes means why?
If any HVDC line is going with positive & negative(the negative usually have return path of current with earthing electrode). Now the question is if this HVDC earthed electrode which is using as return path and earthed any nearby 400kv or 220kv AC substation equipments. which will be the impact of this on AC substation & its equipment, how severe may be this and what should be the minimum distance require between HVDC earthed electrode and AC substation equipments? It's really an high engineering level question...Dare to answer and increase your knowledge.