Which is the best protection in case of shortcircut fuses or mccb ?
Answers were Sorted based on User's Feedback
Answer / wasim
The main difference between circuit breakers and fuses is that circuit breakers can be reset while fuses operate only once and then must be replaced.So MCCB is best.On the other hand Circuit breakers offer an added level of convenience in the event of an inadvertent overload.
Is This Answer Correct ? | 11 Yes | 1 No |
it depends on voltage rating, current rating, and application, for motor, it is better to use fuse, why?. because we can select arcing current and arcing time.MCCB does not have. MCCB suitable only for static load
Is This Answer Correct ? | 1 Yes | 1 No |
what irequirment need to be followed when working on live equipment
what are the problems faiced at dg comissiong
which pump used in WTP explain the function of VFD how to dtermine capacitorbank of capacity one plant
1.what is the funtion of chiller primary & scondary pumps. 2.what is the use of distribution lines & Types. 3.what is the use the thermal power stations & how much capacity.
What is the PI test stand for transformer and what is the producer to do this test?
LT, CC and LMU installed at both the outgoing circuits of 132 kv double ckt transmissio what its means ? and what are there use ?
Why we Specify Transformer rating 433 V Instead of 415V ?
after parallaing two generators current is shooting up in both the generators.for ex: load is 400 kw..after paralling and load sharing current in running gen is approx 900 amps and incoming is 750 amps which is too high when trying toshift the load current in incoming gen is coming more than 1300 amps and both getting tripped and making blackout..
- two pumps must work with them at the same time but if the first pump start the second pump must delayed for some time to start also , with motor rated power = 90 KW and rated voltage = 380 V and rated power factor = 0.85 lag please draw the power and control circuit for it and determine all circuit components parameters that you use it
Why do we avoid electrical conduits in floors at apartments?
What is the basic difference among Circuit breaker,Contractor and Isolator? Are they different names of same device/equipment?
i need list of swg(standard wire guage) or area of conductor v/s current carrying capacity of conductor copper & alluminium...