in transformers for ex. 100mva and 400kv the secondary
current is about 420 amps but for selection of bushing the
capacity of selected bushing is 2000A why there is such
big difference ?
Answers were Sorted based on User's Feedback
Answer / k.prakashchandra
The insulated leads of secondary from the Tr windings are
taken through hollow rods inside the bushing and connected
at the top.As the rod has to bear the all the mechanical
forces like torsion and strain, the wall has to be thick enough.
Is This Answer Correct ? | 0 Yes | 2 No |
Answer / k.prakashchandra
I must have used the word 'pipe' instead of rod.Further,in
the condenser type bushing the oil inside is locked and
isolated from the oil in the tank.Hence it is deprived of
cooling. The pipe should be of much higher capacity to avoid
heating up due to the current flowing through it.
Is This Answer Correct ? | 0 Yes | 2 No |
What is the name of the winding to which supply is given?
how to do the ductor test?
We are designer please help me calculate the size of 11kv cables from step up transformer to M.V panel, total load is 5 mega watt distance 900 feet (used aluminum type cables) please provided formula for calculate the cable with example.
what is electricity
how to calculate busbar size? ex:11000kva main what is the busbar size ?and how to select the correct one
Why Trasformers rated in KVA
13 Answers College School Exams Tests, HAL, Oil and Gas Jobs,
What is the meaning of key single line diagram?
What is Phase to Phase clearance for 800V System Operating Voltage as per IEC61439
what is EIB lighting control system? what is the advantages of this system?
What is the value of nuetral current in star connected load when DC is supplied to it???
plz send me the placement interview question and answers of whizchip(technical and apttitude)..i have an interview in next.
What are the types of transformers according to the arrangement of iron cores?