How do i calculate sizing of transformer on didstrubution
load for high rise building.What should be MVA Rating of MV
Panel feding by 122 kv.
Answers were Sorted based on User's Feedback
Answer / mf.khan
Transformer size can be calculated on Maximum Dammand Load.
For 122KV MV Switchgear fault level should be 350MVA.
Is This Answer Correct ? | 0 Yes | 0 No |
Answer / ravindra
Transformer rating calculated in KVA. We can measure any
transformer rating from its HT & LT Bushing.
Is This Answer Correct ? | 0 Yes | 0 No |