if transformer winding burn on dc supply then
why not alternator rotor winding please post
answer on y.sakhare@rediffmail.com
Answers were Sorted based on User's Feedback
Answer / anil
there should be a relative motion to induce an emf i.e
either a rotating rotor field with dc or alternating supply
to the stationary core in case of transformer if we give
constant dc than there is a constant flux linking with the
secondary which will not produce any emf in secondary and
thus since there is no opposition to the primary emf and
the resistance of winding is very small this will lead to
high currents in primary and thus may lead to the burning
this is not in case of alternator since the rotor is
rotating
| Is This Answer Correct ? | 12 Yes | 3 No |
Answer / yogesh
every conductor produces magnetic field around it when you give ac or dc supply.but in ac supply the flux is alternating which produces self induced emf in winding which opposes supply vtg so currunt limits.but in dc supply there is no self induced emf.so when dc supply given to xmer no self induced emf produced to limit the current and in alternator or dc motor there also no induced emf produced but to limit the current the winding resistance made high ie above 100 ohms wheres xmer wdg resistance is in points range ie 0.1 ohm etc
| Is This Answer Correct ? | 8 Yes | 1 No |
Answer / antaratara ghosh
With reference to the ans#2, the impedance of the
transformer is mostly inductance whereas in sync m/c it is
resistive...so if we apply a dc voltage in trafo, there
will be no inductance and the total impedance becomes very
very small.. thus I=(E-V)/Z will be very high for
trafo...due to this high current trafo windings will burn
but not sync m/c....
| Is This Answer Correct ? | 0 Yes | 2 No |
Answer / k.prakashchandra
The windings in both the cases will not burn out if the
cooling is perfect.When it comes to motors or gen, it is
advisable to specify whether field or armature instead of
just rotor or stator.In case of large HT gen, the field is
the rotor.When Dc is applied and current is =V/DC
resistance.The same with the Tr.At the rated DC current, the
heating in tr will be less as there are no iron losses.
| Is This Answer Correct ? | 0 Yes | 10 No |
a simple c++ program to calculate simple interst with its data members as private
What will be the change in its efficiency and other parameters of a ONAN transformer if it changed to ONAF transformer ?
Advantages of short circuit and open circuit tests of a transformer?
Difference between DOL starter & star Delta Starter? And where the Dol starter used upto how much HP and whereas Star Delta vice versa?
Generator protection &generator test
sir, what is the importance of Fault MVA. how to calculate fault mva of 33kv substation connected by 6.5 km line(single circuit with equal spacing) with 110/11kv transformer in 110kv susbstation.the fault mva on 11 kv bus in 110kv susbstation is 208mva.
What is oscillator circuit?
which type of motor is suitable for water pump?
How can calculate rotor temperature of the alternator? and is there any method to calculate that
basic princple of induction and synchronous motor
what is transformer?
How do you find HT and LT sides of a distribution transformer only by looking at it from outside?
Civil Engineering (5086)
Mechanical Engineering (4453)
Electrical Engineering (16638)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)