What current can be carried by 25 sqmm copper cable safely?
Answers were Sorted based on User's Feedback
Answer / k.prakashchandra
Both the answers are correct except for calculation error in
No. 1.You have to consider IR drop also. Upto 25 m length 4
A/ sq mm and upto 100 m 2.5 A/ sq mm may be taken as
carrying capacities.
Is This Answer Correct ? | 5 Yes | 0 No |
Answer / shantanu mishra
100 Amps. You can take current density as 4 amps per square
mm for copper. For Aluminium cable it can be taken 2 Amps
per square mm. This also depends upon many other factors
such as whether cable is under ground, or burried or
whether it is overhead. tou shouls also takeinto account
ageing factor also.
Is This Answer Correct ? | 5 Yes | 2 No |
Answer / shantanu mishra
I will just make a little correction..." you should also
take into account the derating factor.
Is This Answer Correct ? | 0 Yes | 0 No |
please refer the manufacturer catlog for
this que. but u have to ask that how to
calculate the current carried out in
25sqmm cable ? actully i also dont know
abt the calculation. if any one have
theformula please send iton my mail add.
sandippatel2310@gmail.com
Is This Answer Correct ? | 1 Yes | 1 No |
WHAT IS DC COMPONENT IN CIRCUIT BREAKER?
What is the Difference Between choke & ballast
3 Answers ABB, ICS Integrated Computer Solutions,
Why field resistance is greater than the armature resistance in dc mechine
1 Answers Cape Peninsula University of Technology,
3phase lt motor winding how to checking with megger
Why an ac solenoid valve attract the plunger even though we interchanges the terminal? Will the poles changes?
Brushless excitation of synchronous generators and motors
why the frequency and voltage in india is 230v and 50HZ. when compared to USA say 110v and 60 HZ.
Why ideally the internal resistance of voltmeter should be infinite and of an ammeter be zero
how the aircraft outer body and inner body is separated ?
3 shows a 415 V, 3-phase generator supplying a 3-phase 415/110 V transformer. Draw the individual and combined impedance diagrams to a base of 10 kVA. Determine the system fault kVA and the fault currents at the 415 V and 110 V busbars for short circuit faults on the transformer input or output terminals. Work in p.u. values of impedances.
resistance of transformer oil=?
How to know of any cable size if there are not written on cabl?