Answer / meenakshi

tranformers are rated based on the losses.the two main
losses of a transformer are copper loss n iron loss.copper
loss occurs in transformer whenever it is loaded(full load,
half load or whatever the load may be).thus copper loss
depends on current.but iron loss are constant losses,which
vil always be present no matter the transformer is loaded
or not.thus the total losses of a transformer depends on
volt-ampere n not on the phase angle between them. i.e it
is independent of load power factor.

Is This Answer Correct ?    9 Yes 2 No

why t/f are rated in kva. is it conserned with p.f...

Answer / amit rajak

The transformer is rated in KVA because its efficiency
actully depends on its losses.

and it is known that there are two main types of losses
that occurs in transformer.

They are as follows.
1.iron losses oer hysterisis losses
or Electromagnetic losses
2.copper losses or eddy current losses.

1. iron losses- it generrally occurs at the
windings that is made of copper as conductor and are under
operation . at all the loads and are rated in current
losses.

2. voltage losses-these losses generally occours at
all the time whether at load or not load conditions

so it is clear that this to parameters current and voltage
decides the overall efficiency of the transformers.

and also as the transformers deals with the poiwer in kilos

so it is rated in kilo volt amperes

Is This Answer Correct ?    0 Yes 0 No

why t/f are rated in kva. is it conserned with p.f...

Answer / jameel

the design of windings of transformer depend on the voltage
and current that is meaning kva .
morover the transformer hasnot mechanical output load such
as motor to say the power in kw.
only we calclate iron losses and copper losses in kw.
also the power factor in windings changes according to the
loads which connection in the secondary windings
usually trasformer and generator rated power in kva but the
motor in kw which is the useful power or active power.

Is This Answer Correct ?    0 Yes 2 No

Post New Answer

More Electrical Engineering Interview Questions

what is the purpose of shading ring or shading coil in electrical equipments.

0 Answers   BARC,


As we know multiplicity factor derivation equation is as below MF = main c t ratio / main p t ratio * meter c t ratio / meter p t ratio * meter dial constant Where in digital meters for HT kwh import export now a days meter constant are calibrated already which is 1 So my question is For HT 11kv 110 v line values are as below Main c t and p t ratio are 11000 v and 110 v and 20/5 means 20 amp and 5 amp Now meter values are 11000/√3/110√3 and primary and secondary amp are displayed as -/5 amp on kwh meter so what will be the MF for this meter ?

1 Answers   NEPC,


when we are going to higher voltage level in substations why we are using Sf6 circuit breakers instead of Vacuum circuit breakers.

3 Answers  


what is broken conductor indication

3 Answers   KPTCL,


What happen if two protection core (3p) of VT in LAVT are 11kv/root3, 110v/root3 and one protection core (3p) is 11kv/root3, 110v/3

1 Answers  






What are the types of circuit breakers ?

6 Answers   Genco, Super Max,


what is diffence between synchronus and asynchronus AC motor.?

1 Answers  


Dear all, how we select the cable size according  to current with or without including different correction factor , is there any direct method for sizing of cable... 

0 Answers   Kharafi National,


i have one source transformer with the capacity of 50KVA, connected with two loads 10kw and second one is 15kw.. how can i calculate first load in KVA and second one in KVA .. because Kva rating, power factor rating of of transformer is different from the load… there must be some way to calculate load KVA rating and power factor….

1 Answers  


what is use of capacitor in fan

8 Answers   ABB,


what is multiplying factor of a energy meter connected with a CT ratio of 600/5 and voltage at 415 volts.

1 Answers  


what is static electricity and how it generates?

2 Answers  


Categories
  • Civil Engineering Interview Questions Civil Engineering (5085)
  • Mechanical Engineering Interview Questions Mechanical Engineering (4451)
  • Electrical Engineering Interview Questions Electrical Engineering (16632)
  • Electronics Communications Interview Questions Electronics Communications (3918)
  • Chemical Engineering Interview Questions Chemical Engineering (1095)
  • Aeronautical Engineering Interview Questions Aeronautical Engineering (239)
  • Bio Engineering Interview Questions Bio Engineering (96)
  • Metallurgy Interview Questions Metallurgy (361)
  • Industrial Engineering Interview Questions Industrial Engineering (259)
  • Instrumentation Interview Questions Instrumentation (3014)
  • Automobile Engineering Interview Questions Automobile Engineering (332)
  • Mechatronics Engineering Interview Questions Mechatronics Engineering (97)
  • Marine Engineering Interview Questions Marine Engineering (124)
  • Power Plant Engineering Interview Questions Power Plant Engineering (172)
  • Textile Engineering Interview Questions Textile Engineering (575)
  • Production Engineering Interview Questions Production Engineering (25)
  • Satellite Systems Engineering Interview Questions Satellite Systems Engineering (106)
  • Engineering AllOther Interview Questions Engineering AllOther (1379)