why t/f are rated in kva. is it conserned with p.f.
Answers were Sorted based on User's Feedback
tranformers are rated based on the losses.the two main
losses of a transformer are copper loss n iron loss.copper
loss occurs in transformer whenever it is loaded(full load,
half load or whatever the load may be).thus copper loss
depends on current.but iron loss are constant losses,which
vil always be present no matter the transformer is loaded
or not.thus the total losses of a transformer depends on
volt-ampere n not on the phase angle between them. i.e it
is independent of load power factor.
Is This Answer Correct ? | 9 Yes | 2 No |
Answer / amit rajak
The transformer is rated in KVA because its efficiency
actully depends on its losses.
and it is known that there are two main types of losses
that occurs in transformer.
They are as follows.
1.iron losses oer hysterisis losses
or Electromagnetic losses
2.copper losses or eddy current losses.
1. iron losses- it generrally occurs at the
windings that is made of copper as conductor and are under
operation . at all the loads and are rated in current
losses.
2. voltage losses-these losses generally occours at
all the time whether at load or not load conditions
so it is clear that this to parameters current and voltage
decides the overall efficiency of the transformers.
and also as the transformers deals with the poiwer in kilos
so it is rated in kilo volt amperes
Is This Answer Correct ? | 0 Yes | 0 No |
Answer / jameel
the design of windings of transformer depend on the voltage
and current that is meaning kva .
morover the transformer hasnot mechanical output load such
as motor to say the power in kw.
only we calclate iron losses and copper losses in kw.
also the power factor in windings changes according to the
loads which connection in the secondary windings
usually trasformer and generator rated power in kva but the
motor in kw which is the useful power or active power.
Is This Answer Correct ? | 0 Yes | 2 No |
what is the purpose of shading ring or shading coil in electrical equipments.
As we know multiplicity factor derivation equation is as below MF = main c t ratio / main p t ratio * meter c t ratio / meter p t ratio * meter dial constant Where in digital meters for HT kwh import export now a days meter constant are calibrated already which is 1 So my question is For HT 11kv 110 v line values are as below Main c t and p t ratio are 11000 v and 110 v and 20/5 means 20 amp and 5 amp Now meter values are 11000/√3/110√3 and primary and secondary amp are displayed as -/5 amp on kwh meter so what will be the MF for this meter ?
when we are going to higher voltage level in substations why we are using Sf6 circuit breakers instead of Vacuum circuit breakers.
what is broken conductor indication
What happen if two protection core (3p) of VT in LAVT are 11kv/root3, 110v/root3 and one protection core (3p) is 11kv/root3, 110v/3
What are the types of circuit breakers ?
what is diffence between synchronus and asynchronus AC motor.?
Dear all, how we select the cable size according to current with or without including different correction factor , is there any direct method for sizing of cable...
i have one source transformer with the capacity of 50KVA, connected with two loads 10kw and second one is 15kw.. how can i calculate first load in KVA and second one in KVA .. because Kva rating, power factor rating of of transformer is different from the load… there must be some way to calculate load KVA rating and power factor….
what is use of capacitor in fan
what is multiplying factor of a energy meter connected with a CT ratio of 600/5 and voltage at 415 volts.
what is static electricity and how it generates?