sir,
Two different rating of generator going to connect
parallel, can it set same DROOP or different. Why? Please
explain
Answers were Sorted based on User's Feedback
Answer / sanu chaudhary
droop means speed regulation. if the machine is running at
1500 rpm at no load and the machine came on full load at
1545 rpm this means the droop of the governor is set 3%.so
if the both machine rating is equal hence droop should be
equaland if rating is diffrent ,droop should diffrent for
smooth operation of system .machine of higher rating should
have set less droop then other for equal load sharing
Is This Answer Correct ? | 7 Yes | 0 No |
Answer / n.v.mani
Higher rated machine should be set at less droop than that
of lower rated machine,for equal load sharing and smooth
operation of system.If both machine ratings are equal,droop
should be equal.
Is This Answer Correct ? | 2 Yes | 1 No |