What is the formula to find maximum load of a DG (Single
phase and Three phase)?
Answer Posted / deepak tyagi
For a DG set full load amps. Formula is
kva×1.39
for example
as we have a DG SET of 1500kva than the full load of DG set will be
1500×1.39=2085 Amps.
| Is This Answer Correct ? | 11 Yes | 0 No |
Post New Answer View All Answers
how many joints are allowed in underground HT cable of 1 KM
What are operating procudures & Safety precautions to be observed while operating OLTC in manual mode ?
in a simple IDMT relay we use neutral point of ct for earth fault then what is the requirement of neutral ct and cbct?
How to reduce -234126219.6403 MVAr generation and by what?
what is the calculation formula for motor starting torque,running torque, running torque.
What is 100% protection of generator? Why 100% is not used but 95% is generally used?
how to calculate percentage impedence at 75 deg C at normal tap
Differentiate between digital phase converter and ordinary phase converter.
Why the output of OP-AMP is always less than Vcc?
what is the condition for YnD11
any application of back emf
How to calculate the no of Ceiling fan (1200mm sweep) per unit area?
How do we calculate the Out put voltage of generator, after the excitation is being given?
what is the preventive maintence for ht panels and busbars and vcb abd acb's.
I have 440v power coming to facility,( not being used ) can I buy large generator, (gas) to sell power back to electrical co.