Golgappa.net | Golgappa.org | BagIndia.net | BodyIndia.Com | CabIndia.net | CarsBikes.net | CarsBikes.org | CashIndia.net | ConsumerIndia.net | CookingIndia.net | DataIndia.net | DealIndia.net | EmailIndia.net | FirstTablet.com | FirstTourist.com | ForsaleIndia.net | IndiaBody.Com | IndiaCab.net | IndiaCash.net | IndiaModel.net | KidForum.net | OfficeIndia.net | PaysIndia.com | RestaurantIndia.net | RestaurantsIndia.net | SaleForum.net | SellForum.net | SoldIndia.com | StarIndia.net | TomatoCab.com | TomatoCabs.com | TownIndia.com
Interested to Buy Any Domain ? << Click Here >> for more details...


for commissioning the DPT and Flow Transmitter , what kind
of necessary activities we have to check and do?
specially that orifice flange valve[ isolation valve}



for commissioning the DPT and Flow Transmitter , what kind of necessary activities we have to check..

Answer / carl_ellis

Here's Mr. Emerson's view on loop checking with instructions
for zero checking a DP transmitter on a 3 valve manifold:

Wiring Checkout and Loop Check

The first step in commissioning a new instrument is the
physical installation. The physical installation steps are
the same for both the traditional and new approach:

1. Review P&ID drawings for location and piping instructions.

2. Review device instructions for proper location, mounting,
and piping.

3. Verify field device is physically located in the correct
location per the P&ID. Verify that a permanent tag label is
securely attached to the device that clearly indicates the
assigned loop tag number.

4. Verify field device is correctly connected by performing
the following inspections:
a. Physical inspection- properly mounted and oriented as
designed, ensure close-coupled connections are securely
fastened; pipe stands are structurally sound

b1. Mechanical - Sensing lines, and other process
connections are properly installed, connected and verified
per instrument design specification

b2. For DP transmitters with manifold valves:
- Always perform a zero trim on the transmitter/manifold
assembly after installation to eliminate
any shift due to mounting effects.
- In normal operation the two block valves between the
process and instrument ports will be open and the equalizing
valve will be closed.
- To zero the DP transmitter (3 valve manifold), close
the block valve to the low pressure (downstream) side of the
transmitter first.
- Open the center (equalize) valve to equalize the
pressure on both sides of the transmitter. The manifold
valves are now in the proper configuration for zeroing the
transmitter.
- After zeroing the transmitter, close the equalizing valve.
- Open the block valve on the low pressure side of the
transmitter to return the transmitter to service.

c. Electrical - Conduit runs are properly connected; seal
drains are installed correctly, etc.

5. Verify the input or output signal is within the device's
normal operating range.

6. Verify that any special/custom device characteristics
required are present (example: custom gas curves, special
construction materials, etc.)

7. Measure and adjust associated air and electrical power
supplies.

8. Measure loop impedance by disconnecting the signal wiring
at both the transmitter and rack room ends, shorting the
signal wiring at the transmitter and measuring the loop
resistance with an ohmmeter at the termination panel end.
This process typically takes two technicians with two-way
radios for communication.

9. With an ohmmeter, verify there are no shorts to ground in
the signal wiring by checking the wiring to ground while the
wiring is still disconnected. This process typically takes
two technicians with two-way radios for communication.

10. Verify proper wiring polarity.

11. Connect the wiring to the transmitter in the field and
in the rack room.

12. Verify that all field wiring is properly labeled per the
instrument loop diagram. This includes
all terminations per the instrument loop diagram.

13. Verification that all instrumentation wiring is
mechanically sound by performing a physical "Tug Test" of
the wires.

14. Verify that the field device enclosure is closed, all
temporary shipping stops removed, and the device is
mechanically fit for service as defined above and in the
device instruction manual.

15. Apply power to device.

Is This Answer Correct ?    1 Yes 0 No

Post New Answer

More Instrumentation Interview Questions

Explain the thermocouple and RTD?

1 Answers  


how many parts of valve positioner?

1 Answers   Kentz,


which type inter lock use in petrochemical refinery,and oil & gas?

0 Answers  


In bently nevada vibration monitoring system,what is the reason to maintain the Resistance of the probe + extension cable equal to 95 ohm? If possible explain the basic principle of measurement with detail electronic circuits.

0 Answers   Essar,


what is the name of thermocople element cable from field to pannel end?

3 Answers  


What are different types of orifice plates? State their uses.

0 Answers  


what is the dp across a orifice plate & how much is permanent pressure across an orifice plate.

2 Answers   HPCL,


When a field input to plc is coming from 400 to 600 meters and the input is in 24 V DC? So signal cable of which cross section i should select for proper signal to plc?

5 Answers   Exxon Mobil,


what is the safety integrity levels (SIL)

1 Answers  


how 3 out of 2 Logic/interlocks works? give brief explanation with help of diagram.

0 Answers   Adani Power,


suppose, after calibrating a transmitter we fixed it in a process line. At live zero condition the Tx shows 4.5 mA. what should we do to make the Tx show 4 mA? If we adjust zero, will it not affect the calibration?

4 Answers   ABG Shipyard,


how works encoder in plc

0 Answers  


Categories
  • Civil Engineering Interview Questions Civil Engineering (5086)
  • Mechanical Engineering Interview Questions Mechanical Engineering (4453)
  • Electrical Engineering Interview Questions Electrical Engineering (16638)
  • Electronics Communications Interview Questions Electronics Communications (3918)
  • Chemical Engineering Interview Questions Chemical Engineering (1095)
  • Aeronautical Engineering Interview Questions Aeronautical Engineering (239)
  • Bio Engineering Interview Questions Bio Engineering (96)
  • Metallurgy Interview Questions Metallurgy (361)
  • Industrial Engineering Interview Questions Industrial Engineering (259)
  • Instrumentation Interview Questions Instrumentation (3014)
  • Automobile Engineering Interview Questions Automobile Engineering (332)
  • Mechatronics Engineering Interview Questions Mechatronics Engineering (97)
  • Marine Engineering Interview Questions Marine Engineering (124)
  • Power Plant Engineering Interview Questions Power Plant Engineering (172)
  • Textile Engineering Interview Questions Textile Engineering (575)
  • Production Engineering Interview Questions Production Engineering (25)
  • Satellite Systems Engineering Interview Questions Satellite Systems Engineering (106)
  • Engineering AllOther Interview Questions Engineering AllOther (1379)