After synchronization with grid how to maintain the
power factor in lagging or in leading? if lead of lag what
is the problem?
Answers were Sorted based on User's Feedback
Answer / m.vasudevan
By using a capacitor bank ppower factor lagging or leading
can be maintained. Leadin power factor is the problem. If
Power factor is leading, the reactive power of total power
export to the grid is high and active power content will
become less.
Is This Answer Correct ? | 6 Yes | 0 No |
Answer / k.prakashchandra
Pf lagging means over-excitation ,leading pf is caused by
under excitation.Maintain pf at 0.95 t0 0.98 lagging by
varying the excitation .
Is This Answer Correct ? | 2 Yes | 0 No |
both lagging and leading p.f will badly affect the system
we have to maintin unity p.f.
lagging and leading p.f will take more current from the
alternator for the same equipment.
eg: power taken by a motor = v*i pf
= 230*20*1= 4600 w
suppose if the p.f is .6 either lagg or lead
in order to get the same power to motor it will take more current ie more than 20 amps.
Is This Answer Correct ? | 2 Yes | 3 No |
ratings of lightning arrester
what is the use of CAPACITOR in CFL lamp?
what is the importance of creepage distance in disc insulators
WHAT IS THE DIFFERENCE BETWEEN UNDERVOLTAGE COIL, CLOSING COIL AND SHUNT TRIP COIL OF AN ACB?
Can anybody tell me how to calculate(formula) earth flat size(for copper and aluminium).
how can we run the induction motor at 9000 rpm ,by keeping frequency constant??
is emf is indued if dc is passed through coil
For a Potential Transformer(PT), the primary neutral terminal must be grounded before energization. Why....? What will be heppend if we energize the PT without grounded the primary neutral point? Why..........?
how do we calculate contactor and fuse rating for a motor if its full load current is known,i want exact calculation for 1.5 kw motor????
1 Answers Allied Group, Nucon,
what heppend if we are connected u1-v1-w1 as a star point in the place of u2-v2-w2 in power genration
hi, could someone help me to find a control design for syncronising panel .
WHY CBCT USE ONLY IN Y PHASE NOT OTHER PHASES