I
If i have 2kv ups in which 38Amp *8battries hou many hour's
back up i get from 600Watts
Answers were Sorted based on User's Feedback
Answer / k.prakashchandra
2 KVA UPS, 8 batteries of 38 AH and 12 V and load 600W. The
back up time = 8 x 38 x 12 /600 = 6 Hour (app)
Is This Answer Correct ? | 1 Yes | 0 No |
Answer / kalpesh m. shah
2 KVA UPS, 8 batteries of 38 AH and 12 V and load 600W. The
back up time = 8 x 38 x 12 /600 = 6 Hour (app)
In single phase output voltage is 230V AC so you can
considerd back up time is = ( 8 Batteries X 38 Ah X 12
Volts / 2.6A Load X 230 V Output )X 60% backup = 3.66 Hour
Successfully working.
In Single phase W = V X I
Watt = 600
Voltage = 230
So, Current is 2.6A.
Is This Answer Correct ? | 1 Yes | 0 No |
A distribution transformer giving afrequency of 200HZ, where it is rated for 50HZ. when it will occure?
any idea abt REVERSE METERING concept.........?
what is the mho relay
i applied for c licence with my one year apperents trainee and i have attaced with A grade contractor company experiance that is for 14 monts experiance this document is sufeicant for c licence? pls tell why they rejected
0 Answers TNEB Tamil Nadu Electricity Board,
what are smoke detectors ?
4 Answers Indian Military Services,
how the aircraft outer body and inner body is separated ?
Hp to Kw and Kw to I(amps) conversion......
why do we earth the tandelta point of a power transformer bushing?
what will happen if field winding supply of synch generator accidently got disconnected?
What facility we get after CT secondary earthing and how?
In EHV tranm. The conductors are …….. a) Cu roads b) Cu bars with Si c) Cu tube with Si plate
2 Answers Engineers India Limited,
What are the advantages of using distance protection schemes as opposed to normal overcurrent/ earth fault protection on high voltage feeders.