I
If i have 2kv ups in which 38Amp *8battries hou many hour's
back up i get from 600Watts
Answer Posted / kalpesh m. shah
2 KVA UPS, 8 batteries of 38 AH and 12 V and load 600W. The
back up time = 8 x 38 x 12 /600 = 6 Hour (app)
In single phase output voltage is 230V AC so you can
considerd back up time is = ( 8 Batteries X 38 Ah X 12
Volts / 2.6A Load X 230 V Output )X 60% backup = 3.66 Hour
Successfully working.
In Single phase W = V X I
Watt = 600
Voltage = 230
So, Current is 2.6A.
| Is This Answer Correct ? | 1 Yes | 0 No |
Post New Answer View All Answers
Zone of protection and tripping scheme of arc protection relay.
What is meant by Im=30mA@Vk/2. How to know the kee point voltage for CT design
how many electricity poles are there and what are the names and their sizes.
what happens when series resonance occurs?
What is the basis for selecting Vk/2 or Vk/4 for REF and Differential protection of Transformer and What is the significance of magnetising current
We have a couple of oil tanks at our plant. One of them does not have a lightning arrester installed. My question is it necessary to install an arrestor on every tank or will this particular one be covered by the arrestor installed on the ajdacent tank, Since all the tanks are close to each other. Basically, I want to know that if these arrestors or protection works in a parituclar area of effect or influence. Thanks
what happen when we add mentos in cold drink?& why?
Is it possible to download the Siemens Selection Chart(TYPE 2 coordination) for 1) fuseless selection 2)Fuse selection
why and how current drawn by battery charger depends upon the altitude where it is located?
from which subjects most of the technical que will b asked for hpcl(electrical).pls help me
What will happen if i used 11KV earth ht kit to 11 KV / 11 KV cable termination?
WHAT IS SHORT CIRCUIT STRENGTH OF 100 AMPS MCCB?
The height to which the liquid in a tank to be maintained for a certain constant velocity?
how we calculate torque ? how we improve it ?where torque will either motor or generator ?
What is the different between digital phase converter and ordinary phase converter?