my company total load is 1000kw, 415volt, all load are
inductive load. incoming powerfactor is .8. we want to
have0.95 pf connecting capacitors. so now how much rating of
capacitors we have to connect? show how?
Answers were Sorted based on User's Feedback
Answer / rman
currently, the load is 0.75MVAR operating at 0.8pf. to enhance it to 0.95pf, the MVAR must be decreased to 0.329MVAR.
Q=0.75-0.329=0.36MVAR
0.36MVAR must be your operating reactive power. therefore your capacitance must be {0.36M/[0.36M/(415*0.95*sqrt(3))]^2*sqrt(3)} which will be your reactance at 0.0969 per phase. also to find the capacitor to be inserted per phase,assuming your frequency is 60Hz, C=(2*pi*60*0.0969)^(-1)
therefore the C=27.37mF
| Is This Answer Correct ? | 0 Yes | 0 No |
Answer / rsundareee
your original p.f is 0.8(Tan 0.8) and you required p.f is
0.95(Tan 0.95).Required p.f = kW(Tan0.8 - Tan 0.95),when
you select the breaker rating of Capacitor bank you have to
conside the Hormonics (33%),For exambe breaker rating will
be 100A it shall be (100+33=133) 160A MCCB.
| Is This Answer Correct ? | 0 Yes | 1 No |
why are transformers rated in KVA and not in KW
how to set relay setting? and example calculation...
where we use the SFU & FSU?
what is the relation b/w KW and KWH? plz explain with example.
What do you mean by Stimulastion Test in Diesel Genarator / Why & when it's conducted ?
how many current required for hypo test
wat is the current produced in a 5000v megger? when the positive and negetive terminals are touched on our body get s shock?
why is a avtomatic voltage regulator used for?
Good morning: I'm looking for some informations about the OLTC or the LTC: I wont to know what the function of the tie-resistor in during the operation of reversing/coarse operation Cordially
what is S.T?specify the range?
In secondary transmission i.e., in distribution side, supply for homes are connected through different phases in order to balance the 3 phase load. But in practical we saw nearby house doesn't have power due to single phasing. But other two phases give supply. How it's possible? it doesn't make "single phasing"?
what is the k var ratting of 1250kva
Civil Engineering (5086)
Mechanical Engineering (4456)
Electrical Engineering (16639)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)