my company total load is 1000kw, 415volt, all load are
inductive load. incoming powerfactor is .8. we want to
have0.95 pf connecting capacitors. so now how much rating of
capacitors we have to connect? show how?
Answers were Sorted based on User's Feedback
Answer / rman
currently, the load is 0.75MVAR operating at 0.8pf. to enhance it to 0.95pf, the MVAR must be decreased to 0.329MVAR.
Q=0.75-0.329=0.36MVAR
0.36MVAR must be your operating reactive power. therefore your capacitance must be {0.36M/[0.36M/(415*0.95*sqrt(3))]^2*sqrt(3)} which will be your reactance at 0.0969 per phase. also to find the capacitor to be inserted per phase,assuming your frequency is 60Hz, C=(2*pi*60*0.0969)^(-1)
therefore the C=27.37mF
Is This Answer Correct ? | 0 Yes | 0 No |
Answer / rsundareee
your original p.f is 0.8(Tan 0.8) and you required p.f is
0.95(Tan 0.95).Required p.f = kW(Tan0.8 - Tan 0.95),when
you select the breaker rating of Capacitor bank you have to
conside the Hormonics (33%),For exambe breaker rating will
be 100A it shall be (100+33=133) 160A MCCB.
Is This Answer Correct ? | 0 Yes | 1 No |
how to give earthing in plain?
What is signal flow graph?
Difference between auxliary relay & pla relay
Why does The speed of motor used in elevator remain constant irrespective of load??
what is the function of closing coil in air circuit breaker?
At the starting of dc motor and syn.motor and induction motor high current flowing through the winding. Due to this the windings burnt out. To avoid this different types of starters are used. But incase of transformer what Will be used (At starting no emf is induced in the primary winding)?
why conductors of low tensile strength 1)produce greater sag and 2)can not be used for larger spans
For Synchronisation of DG Sets Sometimes we people use NIC (Neutral Isolation Contactor) Instead of 4-pole ACB or any switchgerar..Please guide me why is it so????
4 Answers Piramal Glass Limited,
what is reactive power (MVAR) and how it is control? how it is generate in powerplant?
Is it possible we are step down 11 kv to 230v ?
what happens when back feeding supply accidently collapses with normal supply ??? How?? [that is sometimes in a substation 11kv feeder if their ws long time permit work, back feeding supply will provide from nearest substation... if accidently after the permit work,they charged the feeder without removing back feeding wat will happen...?]
if dc is better then ac...then why we are perfering ac over dc?eg:at home?