can any one tell me the formula to select the thickness of
wire selection according to ampere rating

Answers were Sorted based on User's Feedback



can any one tell me the formula to select the thickness of wire selection according to ampere rati..

Answer / electrical alie

AWG: In the American Wire Gauge (AWG), diameters can be
calculated by applying the formula D(AWG)=.005·92((36-
AWG)/39) inch. For the 00, 000, 0000 etc. gauges you use -
1, -2, -3, which makes more sense mathematically
than "double nought." This means that in American wire gage
every 6 gauge decrease gives a doubling of the wire
diameter, and every 3 gauge decrease doubles the wire cross
sectional area. Similar to dB in signal and power levels.
An approximate but accurate form of this formula
contributed by Mario Rodriguez is D = .460 * (57/64)(awg
+3) or D = .460 * (0.890625)(awg +3). D can be affected but
the Speed of light c 2.99792458·108 m/s and the
Permittivity of vacuum 00 = 1 / (0 c2)
8.854187817·10-12 C2/J·m

Metric Wire Gauges
Metric Gauge: In the Metric Gauge scale, the gauge is 10
times the diameter in millimeters, so a 50 gauge metric
wire would be 5 mm in diameter. Note that in AWG the
diameter goes up as the gauge goes down, but for metric
gauges it is the opposite. Probably because of this
confusion, most of the time metric sized wire is specified
in millimeters rather than metric gauges. The
Bohr magneton B B = e h / (4 me)9.2740154·10-24 J/T
has been included in these factors.


Load Carrying Capacities
The following chart is a guideline of ampacity or copper
wire current carrying capacity following the Handbook of
Electronic Tables and Formulas for American Wire Gauge. As
you might guess, the rated ampacities are just a rule of
thumb. In careful engineering the voltage drop, insulation
temperature limit, thickness, thermal conductivity, and air
convection and temperature should all be taken into
account. The Maximum Amps for Power Transmission uses the
700 circular mils per amp rule, which is very very
conservative. The Maximum Amps for Chassis Wiring is also a
conservative rating, but is meant for wiring in air, and
not in a bundle. For short lengths of wire, such as is used
in battery packs you should trade off the resistance and
load with size, weight, and flexibility. NOTE: For
installations that need to conform to the National
Electrical Code, you must use their guidelines. Contact
your local electrician to find out what is legal!

Is This Answer Correct ?    2 Yes 0 No

can any one tell me the formula to select the thickness of wire selection according to ampere rati..

Answer / mahesh babu calicut

A log book is available for ch6osing cables at different conditions for different load currents.any how we have to consider voltage drop also in the case of long distance cables(maximtm allowable v.d from mdb to final destination is 5%) if it exceed the limit choose the next higher size. (voltage drop/amps/km for all size of cables available in log book

Is This Answer Correct ?    0 Yes 1 No

Post New Answer

More Electrical Engineering Interview Questions

how much UPS neutral erath leakage current.

0 Answers   HP,


what is the calculation of current when a clampmeter is attached to two phases of any drives.

3 Answers   ABB,


why generaotr rating is in kva and dc motor in kw?

7 Answers   Bhel, NTPC,


which on of the transformer have more core losses and why? 1. Distribution Transformer 2. Power Transformer

5 Answers  


What is the difference between 2 wires RTD's and 3 wires RTD's.Kindly explain the wiring diagram.

1 Answers   QAFCO,






what r substations?what r there work?why voltages r incresed and then reduced during distribution of power

0 Answers  


what are the differenc between vcb and sf6 breakers

7 Answers   Google,


what is the transmission loss for electrical supply? specifically a large shopping complex where the grid is half KM away, what will the % of transmission loss? is there any transmission loss for captive unit generation for above set? thanks

0 Answers  


why are distributed windings generally used in alternators?

0 Answers  


Is there any Institution (Not AMIE)for giving B-Tech/M-tech in Electrical engineering for those who r in service? Give the details please.

2 Answers  


Wtat is mean by GHOAST VOLTAGE?

3 Answers  


Is it possible Z axis excess error alarm reflect in X axis if yes explain ?

0 Answers  


Categories
  • Civil Engineering Interview Questions Civil Engineering (5085)
  • Mechanical Engineering Interview Questions Mechanical Engineering (4451)
  • Electrical Engineering Interview Questions Electrical Engineering (16632)
  • Electronics Communications Interview Questions Electronics Communications (3918)
  • Chemical Engineering Interview Questions Chemical Engineering (1095)
  • Aeronautical Engineering Interview Questions Aeronautical Engineering (239)
  • Bio Engineering Interview Questions Bio Engineering (96)
  • Metallurgy Interview Questions Metallurgy (361)
  • Industrial Engineering Interview Questions Industrial Engineering (259)
  • Instrumentation Interview Questions Instrumentation (3014)
  • Automobile Engineering Interview Questions Automobile Engineering (332)
  • Mechatronics Engineering Interview Questions Mechatronics Engineering (97)
  • Marine Engineering Interview Questions Marine Engineering (124)
  • Power Plant Engineering Interview Questions Power Plant Engineering (172)
  • Textile Engineering Interview Questions Textile Engineering (575)
  • Production Engineering Interview Questions Production Engineering (25)
  • Satellite Systems Engineering Interview Questions Satellite Systems Engineering (106)
  • Engineering AllOther Interview Questions Engineering AllOther (1379)