What is the suitable rating of MCB for 1.5 Ton A.C and why?
1Ton= how many amperes?
Answers were Sorted based on User's Feedback
Answer / manoj kumar sahoo
20 amps is the suitable rating of MCB for 1.5 Ton A.C &
because in starting time it takes 1.5 times more current of
the full load current .1 Ton=09 amps.
| Is This Answer Correct ? | 122 Yes | 32 No |
Answer / smruti
20amp mcb is the perfect rating mcb for 1.5 ton ac due to 1.5 times of stating current.
| Is This Answer Correct ? | 44 Yes | 13 No |
Answer / vishvajeet
Because of compressor at the start current may be more than
5In , but once atrted it will take In only , os 'C' type
mcb only should be refer , now current depends upon the
watt rating so uo to 2.5kw 16 amp MCB can be used but if it
is more than 2.5 kw to 3.5 kw go with 20amp mcb only
| Is This Answer Correct ? | 34 Yes | 13 No |
Answer / ananthanarayanan
For 1.5 ton 1743 w power consumption AC, went with 16 A type C MCB.
Digital domestic House Electric meter showed around 8 Amp current for AC only.
1.5 times 8 is around 12
Hence 16 A is best for power consumption around 1743 W.
| Is This Answer Correct ? | 20 Yes | 7 No |
Answer / gautam lasgotra
For 1.5 ton ac you should use at least a 32 ampere dp mcb.
| Is This Answer Correct ? | 3 Yes | 26 No |
Can we use same copper cable for both AC & DC power.
What are the applications of different multistage amplifiers?Plz also write advantages of these amplifiers? Thaaaaaaaaanx
I am working on a 11KV system with fault current of 40KA for 1 second. I have selected 2500MVA 11/0.433KV transformer. How can i find the impedance value for this transformer? Please help me.
what type of load we can give to motor shaft?
what is subtransient , transient and study state ac components
Are generator action and motor action relates to a particular machine only?
HOW WE CAN REDUCE THE CIRCUIT COMPLEX OF STAR-DELTA STARTER .BECAUSE NOW WE USING ONE TIMER RELAY & THREE CONTACTOR FOR MAIN,STAR & DELTA ?IF ANY IDEAS PLZ POST.THANK U
What is limitedly stable system?
What is the SCR system in drilling rig.
derive DC RMS value for half wave rectifier?
Define noise?
suppose generator rating is 50 kw,load is 25 kw,hw much d generator ll generate?what about d remainin power?
Civil Engineering (5086)
Mechanical Engineering (4456)
Electrical Engineering (16639)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)