To test Transformer we give HT side 440V to see wheather
that it is producing 17.6V on LT to verify Voltage ratio is
correct or not but when we give the 440V voltage to LT side
then what will happen to HT voltage ?
Answers were Sorted based on User's Feedback
Answer / manohar mishra
For ratio test, only the change in voltage is to be measureD. If 440 V is fed to LV, HV voltage will go to a HIGH VALUE (11kV) making it difficult to measure. Blowing of fuses do not occur as there is no flow of current.
| Is This Answer Correct ? | 6 Yes | 0 No |
Answer / nithi
For ratio-test,the second answer may be correct.
But at the same time,if we apply high voltage in LV
side (in ratio-test also)for a longer period (in seconds),
LV winding cannot withstand, result in insulation break-
down,blown-out of fuses.
generally ratio-test is conducted with the
specified (allowable) voltage magnitude.so,practically this
much of voltage is not applied for LV side.I hope,this
answer will be correct.
| Is This Answer Correct ? | 2 Yes | 0 No |
Answer / nithi
Nothing will happen.Simply,fuse will blown-off.
REASON: LV windings normally have low resistance (fatty
winding) compared to HV side.so, at the moment of
application of high voltage the fuse will sacrifice itself
to pretect the transformer LV windings.
| Is This Answer Correct ? | 0 Yes | 4 No |
what is over frequency protection
Myself completed B.Tech ECE in private university but i am working as an testing and commissioning engineer in electrical field whether i am eligibility to apply electrical licence.
My load is 1635 KW. & current pf is 0.884, I have to improve it for 0.99.Please suggest what KVAR value is needed?
how many types of colling system it transformers?
what happens when d cexcitation given to alternator is removed while it is running or what happens when dc excitation is failed in alternator while running?
how to calculate cable size with respect kw
what is Fault level? why it is calculated? how will u decide same for our plant?
For 415v,3phase,22kw rating of motor how to calculate MCCB rating
when any relay trips in any ckt then what type of setting is there in motor?what is function of relay in that ckt?
Why should we use the igniter in the sodium vapour lamp.
7 Answers ABB, Delphi, Mudhra, NTPC, PICT,
what is the formula to convert from KVAr to current?
1 Answers Halcrow International Partnership,
HOW THE OLTC TRANSFORMER SAVE ENERGY IN COMPARISON TO OFF LINE TRANSFORMER AND IS IT ECONOMICAL TO REPLACE THE OFF LINE TRANSFORMER TO OLTC TRANSFORMER
Civil Engineering (5086)
Mechanical Engineering (4456)
Electrical Engineering (16639)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)