what isthe emf eqation of a transformer
Answers were Sorted based on User's Feedback
Answer / reshi
Emf in primary
E1=4.44fN1BmA
Emf induced in the secondary
E2=4.44fN2BmA
Bm -flux density in weber /sq m (Tesla)
A-net cross sectional area of core in sq m.
| Is This Answer Correct ? | 12 Yes | 5 No |
Answer / loki
E=4.44*A*B*N*f
where A=area of cross section of core
B=fux density
N=no.of turns
f=operating frequency
| Is This Answer Correct ? | 6 Yes | 0 No |
Answer / anil bhatia
sorry my earliar reply there was a mistake ignore it .
new reply
Emf in primary
E1=4.44fN1Bm
Emf in secondary
E2=4.44fN2Bm
where Bm is maximum /peak flux density, in weber /sq m
(Tesla)
under no load condition E!=v1, E2=v2 , assuming negligible
Magnetizing current.
equation is v=4.44FNBm
or say V/N= 4.44FBm
1) Thus reduction in frequency F causes the increase in
flux and their by flux density.
2) Thus increase in volt/turn , V/N causes increase in the
flux and thereby flux density.
| Is This Answer Correct ? | 0 Yes | 0 No |
Answer / anil bhatia
Emf in primary
E1=4.44fN1Bm
Emf in secondary
E2=4.44fN2Bm
where Bm is maximum /peak flux density, in weber /sq m
(Tesla)
under no load condition E!=v1, E@=v2 , asuming neglesible
magnetising current.
equation is v=4.44NBm
| Is This Answer Correct ? | 0 Yes | 1 No |
Answer / malvik
e= 4.44 f Bm Ai Kw Tph
wer Kw is winding factor
Tph is turn per phase
Bm is maxflux density
Ai area of iron part
| Is This Answer Correct ? | 5 Yes | 7 No |
As per BIS, Earth pit resistence value?
How do i perform grounding of star point of Genset (400V) for making connection with step up transformer of DELTA-DELTA (400V to 20KV) ? while Genset itself has its own neutral and grounding bus bar inside genset breaker box whereas we have another neutral and grounding busbar in synchronizing panel next to genset at maximum distance of 6meter, would someone pls advice if we can only perform neutral grounding in synchronizing panel or should we ground neutral on both places inside genset breaker box and synchronizing panel.
what is first pole to clear factor
how do we calculate cable sq mm size,that if 50 A load
132 KV TRFO BUSHING CT BURNT WHEN A 6.6KV HAS BEEN APPLIED TO IT .WHY .ANY REASON ?
what is the CT & PT. where is it uses.what is the using that plese kindly answer me...?
what happens if earth of 33kv cable is not connected to earthing pits? please send this query's answer to ngrm.sudha249@gmail.com
The Howland current source produces a A Unidirectional floating load current B Bidirectional single-ended load current C Unidirectional single-ended load current D Bidirectional floating load current
IR value for 30kw lt motor
which Machine u will prefer to use at place where Flammable gases are coming out & why ??
What is the difference between Earthing & grounding
Dear all, is ther any body who can tell me about the setting of ACB(air circuit breaker ). what kind of it,s setting is and how to do it,s setting. also please tell me the setting of VCB(vaccume circuit breaker) . please tell me their setting,s. i will b very thank ful to all of u. Thank,s and Regard,s. Muhammed Ikram.
Civil Engineering (5086)
Mechanical Engineering (4456)
Electrical Engineering (16639)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)