Answer / karthik
Watt is the product of voltage, current and power factor.
VA is the product of voltage, current and power factor.
Motor is an inductive load and operates at a power factor
less than unity. So the current drawn by it is more than the
apparent at constant power.
For a 3ph motor, P=√3*V*I*cosø where V,√3 are constants.
At constant P, I*cosø is also a constant. if pf cosø
varies, I too varies. i.e. if pf is poor (cosø reduces), I
increases. Hence rating needs to be specified in KW.
Whereas for a generator, it isn't a load. It supplies power
to a load. So power factor doesn't come into picture. Hence
its rating is specified in KVA.
| Is This Answer Correct ? | 11 Yes | 2 No |
Answer / shahulsnfa
See, KVA is apparent power which means the power
available. and KW is real power which means how much power
utilised from available power.
motors are utility machines which consumes the power
from the source for its working. and the generator are
producers and not consumers. the motor consumes the power
in terms of voltage and current.
when phase angle difference btwn current and voltage
is zero, then KW=KVA. but the phase angle difference
between current and voltage will have some value regarding
load. so the real power is determined by the load and not
by the source.
that is why macines are rated in KW and generators are
in KVA. and the transformers are transforming power rather
than consuming.. so they also rated in KVA.
| Is This Answer Correct ? | 11 Yes | 2 No |
Answer / navmit bhimani
In transformer there are two losses,copper loss depend on
current and iron loss depend on voltege and nothing
relation with power factor.so and so....
| Is This Answer Correct ? | 8 Yes | 1 No |
Answer / vinamra
generator and the transformer is not a load,means its power
fector is not decided,its pf is depend upon the loads which
will connect to the gen. or trans.,therefore it rating is
in kva.but in case of motor its power fector is predecided
so its rating is in kw
| Is This Answer Correct ? | 4 Yes | 0 No |
We buy/fix a motor to do a specific job.Job done is measured in watts.So a machine say a pump will use up to 3 KW to run as designed than we fix a motor of 3KW or slightly bigger to run it.Now the motor is 3KW or bigger say 30 KW and the voltage is AC or DC operated is up to you.
generators are rated in KVA because we dont know at what pf will it be operated. Say you have fitted a pf correction board to maintain at 0.95pf, you dont have a guarantee it wont breakdown or take some time to adjust. What is important the generator voltage is constant and the generator dont trip or burn.So if the pf can change anytime the current also can change anytime this may make your generator to trip on overcurrent,overvoltage(leading pf)or even destroy your genset.By rating your generator by KVA with a constant designed voltage you can know the maximum current the genset can give irrespective of pf.It is a safer and sure way of protecting your generator.you can even load yor genset at 0.2 pf so long you dont exceed the rated amps or KVA.
| Is This Answer Correct ? | 1 Yes | 0 No |
Answer / expert
when kva is calculated pf comes into play, and not in KW.
as we know that the tranf and DG pf is dependent on the
load,but the motor draws an constant power with specified
pf..........if not clear plz reply
| Is This Answer Correct ? | 4 Yes | 11 No |
What are the different methodes for calculating the short circuit Current?
What do you mean by deregulated power system structure? Which structure (regulated/deregulated) is used by modern power system?
y we are used signal conditioner in capacitive transducer
We are getting supply at33kvand it stepdown to 11kv.So Our requirement is 11kv voltage.why we draw 33kv from the grid instead of 11kv?
How much must be gape bitween 2 cable on cable tray?
How can we calculate No load and full load torque of electrical machines, i.e. motor or alternator?
what is DG synchronization panel plz explain the working!!!!!!!
12 Answers Kirloskar, Lanco, MPS Techologies, Sedemac,
what is meant by directional earth fault and non directional earth fault? describe both.
In scott connection why connect teaser transformer to 86.6% and main transformer to 50%..
For 132 KV line, PT or CVT which is prefered for measuring & protection? is there any IS or IEE standard available?
HI,how to know that the MEGGER which i am using is working properly,reply....thankyou
What is float cum boost charging system?
Civil Engineering (5086)
Mechanical Engineering (4453)
Electrical Engineering (16638)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)