Any one can explain if there is any harm from humming noise
heard from air circuit breaker : we have 415 switch board
having two incomers from transformers 3.3KV/415V , when bus
coupler closed, and open one ACB incomer to work in one of
the transformers, the current started hunting around 50
Amps, and heard humming noise from the air circuit breaker,
although the load current was only 1200 amps while the ACB
capacity is 2500 Amps, and the transformer 1600 KVA. The
same didn't happen when taken the other transformer offline.
Why this humming noise and current fluctuation? is there
any implication or danger, bearing in mind that we just
returned everything back to normal and stopped the
maintenance of the transformer. Shall we go ahead and
ignore this noise?
Answers were Sorted based on User's Feedback
Answer / vijendra joglekar
First of all do you know what is the reoson for using
Circuit breaker in electrical equipment/device means it
will protect the device whenever the fault occurs it will
trip the breaker or open the contacts ( fixed /moving
contacts).And you told that there is some humming sound is
there in CB that means it will harm the equipment (may
chance to fire) just you need to check whether all the
contacts/connections in the breaker/device is tightly
connected by loose connections also you getting these type
of errors/faults even tho the current rating is samall (
you told 50A)
You need to check:
1.Tightness (mandotary)
2.Check the calibration of the equipment
2.Check the technical specification (i know you already
checked before installing)
Go ahead dont stop the work if you are still getting sound
means u just repalce the breaker unless why u r taking risk.
| Is This Answer Correct ? | 5 Yes | 1 No |
Thanks Vijendra Joglekar
The breaker has been serviced already and nothing wrong
found, the load is 1200 Amps, but the current fluctuation
is around 50 Amps (+&- 25Amps)when load increased, the
sound started at load above 800 Amps, while the breaker is
rated up to 2500 Amps.
| Is This Answer Correct ? | 1 Yes | 0 No |
Answer / yusuf
Can you tell me what is the circuit Breaker settings like
overload,shortcircuit,ground fault & Instantaneous s/c
settings.Acc to your details max load that can be derived
from X'mer is 2228.56 amps & from 800 amps onwards Breaker
is creating this problem.So around from 25% load CB is
creaing problem also tell me about any release installed
(Closing,shunt,undervoltage).
| Is This Answer Correct ? | 0 Yes | 0 No |
This is an old breaker and has no protection devices, close
and open manually. closes by operating rod and opens by
trip button. Protection in the HV side of the transformer
incomer. I suspect the contacts got wear and tear due to
long time service and intending to change the fix and
moving contacts. Small gaps ( not seen by eyes) between
contacts could cause this sown as far as I know.
| Is This Answer Correct ? | 0 Yes | 0 No |
Answer / yusuf
Yes,it can be.A very small gap can't seen by naked eyes
between CB main contacts could create this problem.Exactly
from which area this sound is comming? Is is some Clicking
sound/Buzzing sound.Can u give me Breaker details like make
(Siemens/L&T/ABB/Scneider) & Type no, 3pole/4 pole any
neutral earth fault protection provide extra to the
breaker,two breaker earthing & neutral connection.I am
talking of two main transformer breaker.Please furnish some
details to rectify the problem.
| Is This Answer Correct ? | 0 Yes | 0 No |
What are various impedence in any machine
2 Answers Engineers India Limited, NTPC,
Why TAP changer provided in primary side of HT transformer ? and why not in secondary?
i need to calculate high voltage line power factor daily basics but there is meter reading kwh and kvah while calculating power factor kwh/kvah formula was right. for examble there is point c=13kwh c=1.8 lag c=1.2 lead and c=14.5kvah like that i know that p.f =kwh/kvah but c=1.8lag kvarh and c=1.2lead kvarh points i dont know if u know please reply
Define conversion efficiency of a power amplifier. What is its value for class c power amplifier?
how to find out this one mcb r mccb?
Please tell me the earthing procedures adopted for the STAR-STAR 3 Phase transformer in india and give a better sugession for earthing
WHAT IS REACTIVE POWER?
how to Select its CORE in electrical cables based on its applications? or Application of various types of electrical cable based on it CORE?
what is neutral ground resistance relay? how it is helpful in protecting system?
When a single pase capacitor run motor- run on 230vac and Case(1)run with 8 Mfd 250 vac.capacitor , Case( 2) run with 8 Mfd 400vac capacitor. What is difference between both case regarding power ,efficiency etc?
What is different between Circuit breaker and Isolater?
What is IDMT relay how it works.
3 Answers Electrotherm, Sulzer,
Civil Engineering (5086)
Mechanical Engineering (4456)
Electrical Engineering (16639)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)