Answer / hareesh
CTs have two fuction one is metering & othjer is protection.
for metering CT (0.1, 0.2 ,0.5,1.0 etc class).that means
error of CT has some tolerence limit. if u r using a 0.2
class CT (500/1A).at 500A ur CT error shud exceed more than
0.2%. i.e class represent some allowable limitation of
error in the ct. so CT shud not exceed this error.choosing
the type of class depends upon application. if u want more
accurate measurement u shud go for 0.1 class CT. tariff
calculation based on CT n PT reading.. if u dont have
better accuracy.. ur calculation of tariff also wont be
accurate. protection CT classes are( 5P,10P,PS etc)this
deals with CT saturation characteristics. like metering CT
this is also have some tolerence limit.thats wht we call
class
| Is This Answer Correct ? | 11 Yes | 2 No |
transformers? power factor? machiences?
Why mostly conductor made by 7 nos wire?
What is negative sequence over voltage element?
THE 40 MW OF POWER FOR 220 V III PHASE POWER CONNECTION REQUIRES HOW MANY KVA POWEER REQUIREMENTS
7 Answers Chartered Accountant,
How to reduce -234126219.6403 MVAr generation and by what?
why ct ,cvt should be stored in a vertical position?
How can we measure the frequency of a rotor running in full load condition? Explain the method of measuring.
how much air gap in induction motor as per the Indian standards?
Why neutral is used in electrical system?
Three set (each phase contain 2 cable of 400 mmsq CU XLPE AWA) of single core cables are connected to 11 KV motor of 14 MW & the switch gear supplay is taken from 11kv feeder & this supplay taken from 275 KV substation. Problem is one pair cable(L3- 2 cable ) getting very hot & gland melted and damaged in switch gear side. the other two cable haven't any more hot(ambient temp only & L3 haveing 95- 100 Degree C. The same problem happened in 275 KV substation switch gear side also where the supply taken for 11 kv switch gear. But here L2 phese cable had problem. Why it is happening like this?. The cable having temperature different at different location from gland side inthe case of 11KV feeder of 275 kv substation. why ?
What is the current flow in 230v ac supply ? What is the current flow in 415v Ac supply ?
In distribution transformers, fuse wires are very thin when compared to conductor size. How it's possible?
Civil Engineering (5086)
Mechanical Engineering (4456)
Electrical Engineering (16639)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)