Resistance Grounding falls into two categories: Low
Resistance and High Resistance
1) In Low Resistance Grounded (LRG) Systems the current is
limited to 25 amps or more. Generally the range is from 25
to 600 amps, although in some systems it may be even
greater.
2) In High Resistance Grounded (HRG) Systems the current
is limited to 10 amps or less.
------------
A) On systems with a voltage of 1000 volts or less (phase-
to-phase) grounding resistors are not used. Normally these
system use a solidly grounded configuration with no
intentional impedance being introduced into the system.
B) Resistance Grounding is recommended on Medium Voltage
Systems from 1000 volts to 15,000 volts phase-tophase.
C) Because of the cost, Resistance Grounding is not usually
used on systems above 15,000 volts phase-to-phase.
Additionally, the use of a solidly grounded system allows
for use of equipment which is insulated for the
phase-to-neutral voltage of the system.
·D) When a system has protective relays which will trip the
circuit if a ground fault occurs, a grounding resistor with
a 10 Second Rating is often specified, because the relays
will trip the system in less than 10 seconds.However, One
Minute or Ten Minute ratings are sometimes used for an
extra margin of safety, even though the cost will be
greater.
| Is This Answer Correct ? | 5 Yes | 0 No |
Resistance Grounding falls into two categories: Low
Resistance and High Resistance
1) In Low Resistance Grounded (LRG) Systems the current is
limited to 25 amps or more. Generally the range is from 25
to 600 amps, although in some systems it may be even
greater.
2) In High Resistance Grounded (HRG) Systems the current
is limited to 10 amps or less.
A) On systems with a voltage of 1000 volts or less (phase-
to-phase) grounding resistors are not used. Normally these
system use a solidly grounded configuration with no
intentional impedance being introduced into the system.
B) Resistance Grounding is recommended on Medium Voltage
Systems from 1000 volts to 15,000 volts phase-to phase.
C) Because of the cost, Resistance Grounding is not usually
used on systems above 15,000 volts phase-to-phase.
Additionally, the use of a solidly grounded system allows
for use of equipment which is insulated for the phase-to-
neutral voltage of the system.
D) When a system has protective relays which will trip the
circuit if a ground fault occurs, a grounding resistor with
a 10 Second Rating is often specified, because the relays
will trip the system in less than 10 seconds. However, One
Minute or Ten Minute ratings are sometimes used for an
extra margin of safety, even though the cost will be
greater.
| Is This Answer Correct ? | 3 Yes | 0 No |
Answer / john
HRG - High resistance grounded.
LRG - Low resistance grounded
| Is This Answer Correct ? | 2 Yes | 0 No |
Sir We have a REF relay connected to 10MVA(Y-Y) Transformer.on External earth fault REF relay trips along with earth fault relay.The REF relay has no complant as we tested relay.Why is it happening?
WHAT IS THE difference betwwen LT CABLE AND CONTROL CABLE
How convergengr of nr method is not dependent on selection of slack bus and how gauss siedel method depends?
What is slip in an induction motor?
What happens to a line-frequency of high-frequency transformer when it is first energized/ re-energize?
Explain Even and Odd signals?
Car battery + terminal allways biger than - terminal! Why?
why power not passes in plastic and rubber material
how capacitor buield up the voltage
what is two wattmeter test
Why r use in the tap changing x' mer.
There is one 40MVA oil cooled transformer (yet to commission), filled with 95% oil and we are trying to fill 5% Nytrogen in that transformer so that there should not be any foreign component inside. But even though there is no leakage, nytrogen is not withstanding inside transformer, within a day or two pressure guage is showing 0. Why is it soooo? Pls reply.
Civil Engineering (5086)
Mechanical Engineering (4453)
Electrical Engineering (16638)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)