How the neutral earthing is connected in DG alternator
Answers were Sorted based on User's Feedback
Answer / niti
alternator star point should be given to double earth.
Is This Answer Correct ? | 16 Yes | 7 No |
Answer / vinod.c
Yes,this is correct Answer.Ther is 2 Neutral Earthing.
And also 1 Body Earthing is necessary.
Is This Answer Correct ? | 7 Yes | 0 No |
Answer / saravanan
if the 3 phase supply is balanced(ir+iy+ib=0) that time only
you earthed the mid point of earth else you must use some
proper earthing methods like resistance earthing,plate
earthing like that...
Is This Answer Correct ? | 8 Yes | 3 No |
Answer / ram singh
DG Neutral earthing should be connected after neutral
contactor connected towards load side because to avoide
neutral neutral failure to load side which is danger incase
of neutral contactor contact tips carbonise or breakes.
Second reason is to balance load during synchronising.
Third reason is to install REF.
Is This Answer Correct ? | 4 Yes | 3 No |
how does ELR works? explain
During the testing of Electrical Equipment the test cables should not touch the equipments. For that testing engineers use to cotton rope to hang the cable from measuring Equipment to testing equipment terminal. Please explain the technical reason for this practice.
The Howland current source produces a A Unidirectional floating load current B Bidirectional single-ended load current C Unidirectional single-ended load current D Bidirectional floating load current
what are the types of transformers
what is the contact resistance of vacume circuit breaker??
What is meant by Load Encroachment in OHL Feeder Protection?
what is the earth resistance
why nearly all the voltage levels are in the multiples of 11 like 3.3 ,6.6 ,33 ,11 kv.....
We have three 33kv substations. All of them energised by same source.When i am checking the phase sequence between one substation to other substation (like R Phase to R Phase) by multimeter i am getting some voltage.Near to LT panels UPS panels are there. Can u explain whether any possible to happen like that. In Phase SEquencemeter is showing correctly in both substations. How is it happen. Explain me.Explain me communication signal will produce Phase difference on this case.
why neutral is neccessary?
What are the parameters of water ( Water quality )to be monitored in Centralised HVAC ( water cooler chillers )
is it true there's a big difference in using Cummins or Denyo...especially power output or leakage