in 3 phase (4 wire) star connection - is current pass through
neutral??
Answers were Sorted based on User's Feedback
Answer / asdf
Only if there are unbalanced conditions between the 3 phase lines.
| Is This Answer Correct ? | 15 Yes | 0 No |
Answer / md. obaydur rahman
We know that,in a star connection for balanced condition the
phasor sum of three line current is zero. As a result in
balanced condition there is no neutral current. But in
unbalanced condition the sum is not zero and a current is
flowed through the neutral wire.
| Is This Answer Correct ? | 7 Yes | 1 No |
Answer / ankush miglani 9718037333, eba
for star connections if the load is balanced, the phasor
sum of the three currents is zero.
but if the load is unbalanced, the all three phases do not
carry the same load or if there is any fault, a current
passes thru the neutral and the amount is equal to the
current that balances the all three phase currents.
| Is This Answer Correct ? | 6 Yes | 0 No |
Answer / srikanth
Yes.. current passes through neutral because it is not
balanced load or connection.... due to this current will
pass...
| Is This Answer Correct ? | 2 Yes | 0 No |
Answer / theravikumaran
i think, answer is no... but i don't know why
| Is This Answer Correct ? | 6 Yes | 10 No |
how to calculate the megger values for motor, cables and transformers?
In Air circuit breaker LSIG protection unit is used. Without fault in cables (2 runs 3Cx150Sq.mm Copper, 1Kv grade, XPLE armored cable IR value is more than 550Mohm @ 500V Megger) and load section Long time Overcurrent protection is triggers and trips the unit. We changed LSIG protection with new factory tested unit. Even then fault is persisting. Please suggest the possible causes
why in power staions distriution r like 11kv,33kv,66kv in india?
Inductor and capacitor........power in one phase and ...... in it another phase.
why induction motor speed is decress with increase in load? how synchronous motor speed is constant?
Can earth resistance be measured without connecting the earth electrode? and should earthing connections be disconnected What is the effect of connecting two cables of different sizes in parallel with supply? Thanks in Advance. I am intrested to get in touch with some tecnocrats/engineers,my mail i.d is : hiremathvijay@rediffmail.com
Slip at maximum torque depends on A rotor resistance and reactance B stator reactance C load current D stator resistance
why ht cable end termination don't have a gland?
What is the Working principle of ELCB and RCCB?
What is the 415V AC Soft starter? Explain with an example?
how to calculate multiplying factor with ct ratio 400/5
Determine the MVA rating of the power transformer given that 110/66 kV,1000 Amps. Folks how can i calculate the MVA rating with this Data??Plz Help........
Civil Engineering (5086)
Mechanical Engineering (4453)
Electrical Engineering (16638)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)