Determine the MVA rating of the power transformer given
that 110/66 kV,1000 Amps.
Folks how can i calculate the MVA rating with this Data??Plz
Help........
I have taken 66kv 1000A and pf as 0.85
MVA=MW/pf so firsrt we must calkulate MW
MW=(1.73*66*1000*0.85)/1000
=97MW
MVA=MW/pf
=97/0.85
=114 say 120MVA
There is no single transformer for 120MVA
so you can use 3*40MVA Transformers in parral operation
| Is This Answer Correct ? | 22 Yes | 2 No |
what is electronic regulator and how we can use that in fans?
What is the difference between 2 wires RTD's and 3 wires RTD's.Kindly explain the wiring diagram.
How to take vector group test for Ynd11 transformer.
What are the disadvantges of leading power factor
How CT & PT ratings are decided for a 11KV or 33KV transmission line?
Why restricted earth fault protection is needed? Why can’t differential Protection is sufficient?
What is force on parallel conductors ?
what is diff btw electric,magnetic & eletromagnetic field
A Generator is in running condition and Rotor earth fault alarm is coming.How to check on line(i.e in running condition) whether there is actual earth fault in rotor or not.
What type of a DC motor would you use for a lift?
HOW WE CAN REDUCE THE CIRCUIT COMPLEX OF STAR-DELTA STARTER .BECAUSE NOW WE USING ONE TIMER RELAY & THREE CONTACTOR FOR MAIN,STAR & DELTA ?IF ANY IDEAS PLZ POST.THANK U
how to discharge 3 phase power factor correction capacitors
0 Answers M S Ramaiah Institute,
Civil Engineering (5086)
Mechanical Engineering (4456)
Electrical Engineering (16639)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)