Golgappa.net | Golgappa.org | BagIndia.net | BodyIndia.Com | CabIndia.net | CarsBikes.net | CarsBikes.org | CashIndia.net | ConsumerIndia.net | CookingIndia.net | DataIndia.net | DealIndia.net | EmailIndia.net | FirstTablet.com | FirstTourist.com | ForsaleIndia.net | IndiaBody.Com | IndiaCab.net | IndiaCash.net | IndiaModel.net | KidForum.net | OfficeIndia.net | PaysIndia.com | RestaurantIndia.net | RestaurantsIndia.net | SaleForum.net | SellForum.net | SoldIndia.com | StarIndia.net | TomatoCab.com | TomatoCabs.com | TownIndia.com
Interested to Buy Any Domain ? << Click Here >> for more details...


Determine the MVA rating of the power transformer given
that 110/66 kV,1000 Amps.

Folks how can i calculate the MVA rating with this Data??Plz
Help........



Determine the MVA rating of the power transformer given that 110/66 kV,1000 Amps. Folks how can..

Answer / shanu shamsudeen

I have taken 66kv 1000A and pf as 0.85
MVA=MW/pf so firsrt we must calkulate MW
MW=(1.73*66*1000*0.85)/1000
=97MW
MVA=MW/pf
=97/0.85
=114 say 120MVA
There is no single transformer for 120MVA
so you can use 3*40MVA Transformers in parral operation

Is This Answer Correct ?    22 Yes 2 No

Post New Answer

More Electrical Engineering Interview Questions

what is electronic regulator and how we can use that in fans?

3 Answers  


What is the difference between 2 wires RTD's and 3 wires RTD's.Kindly explain the wiring diagram.

1 Answers   QAFCO,


How to take vector group test for Ynd11 transformer.

2 Answers   Voltech,


What are the disadvantges of leading power factor

5 Answers  


How CT & PT ratings are decided for a 11KV or 33KV transmission line?

3 Answers  


Why restricted earth fault protection is needed? Why can’t differential Protection is sufficient?

3 Answers  


What is force on parallel conductors ?

0 Answers  


what is diff btw electric,magnetic & eletromagnetic field

0 Answers   Senthil,


A Generator is in running condition and Rotor earth fault alarm is coming.How to check on line(i.e in running condition) whether there is actual earth fault in rotor or not.

4 Answers  


What type of a DC motor would you use for a lift?

0 Answers   GE,


HOW WE CAN REDUCE THE CIRCUIT COMPLEX OF STAR-DELTA STARTER .BECAUSE NOW WE USING ONE TIMER RELAY & THREE CONTACTOR FOR MAIN,STAR & DELTA ?IF ANY IDEAS PLZ POST.THANK U

0 Answers  


how to discharge 3 phase power factor correction capacitors

0 Answers   M S Ramaiah Institute,


Categories
  • Civil Engineering Interview Questions Civil Engineering (5086)
  • Mechanical Engineering Interview Questions Mechanical Engineering (4456)
  • Electrical Engineering Interview Questions Electrical Engineering (16639)
  • Electronics Communications Interview Questions Electronics Communications (3918)
  • Chemical Engineering Interview Questions Chemical Engineering (1095)
  • Aeronautical Engineering Interview Questions Aeronautical Engineering (239)
  • Bio Engineering Interview Questions Bio Engineering (96)
  • Metallurgy Interview Questions Metallurgy (361)
  • Industrial Engineering Interview Questions Industrial Engineering (259)
  • Instrumentation Interview Questions Instrumentation (3014)
  • Automobile Engineering Interview Questions Automobile Engineering (332)
  • Mechatronics Engineering Interview Questions Mechatronics Engineering (97)
  • Marine Engineering Interview Questions Marine Engineering (124)
  • Power Plant Engineering Interview Questions Power Plant Engineering (172)
  • Textile Engineering Interview Questions Textile Engineering (575)
  • Production Engineering Interview Questions Production Engineering (25)
  • Satellite Systems Engineering Interview Questions Satellite Systems Engineering (106)
  • Engineering AllOther Interview Questions Engineering AllOther (1379)