we all know that in transformer, voltage and current are
inversely related i.e. Vp/Vs= Is/Ip....so in standard
CT..we have a ratio of 200/5...that means our voltage
should increase by ratio of 40..althoug that is not the
case...because that requires high insulation level.and
pratically not feasible......can anybody clarify my
ques.......thanx
Answers were Sorted based on User's Feedback
Answer / k.prakashchandra
Voltage ratio is not applicable when the secondary of the Tr
is short circuited.Actually the secondary of CT has more
turns than the primary.No voltage is applied to primary of
CT and a small voltage is induced in secondary due to the
mmf created in primary by the current flowing through
it.When this emf of secondary is short circuited , the
current produced is proportional to the current in the
primary.That is why it is called CT and not just Tr.
| Is This Answer Correct ? | 3 Yes | 2 No |
Answer / peter b
Current and voltage and still inversely related in a CT.
However, the primary of a CT does not see the full line
Voltage i.e. a CT on a 110kV bus does not have a primary
Voltage of 110kV! The CT's primary is in series with the
main load; the primary voltage of the CT is simply the
induced Voltage due to the AC flowing through the primary.
This Voltage is only a tiny fraction of the full line
Voltage. The only insulation requirement is that the CT as
a whole be insulated from neutral/earth. That's why they
are mounted on long insulators.
| Is This Answer Correct ? | 0 Yes | 0 No |
An alternator is started without excitation then how much voltage it will produced at strating at full rpm??
1. what is the power factor of a purely inductive load? (i) Zero (ii) Lagging (iii)Leading (iv) Unity 2. which type of transformer connection is preferred in case of power supply transformer? (i) Star/Star (ii) Delta/Delta (iii) Star/Delta (iv) Zig Zag/Star
with out name plate details , how to find the metering ct and protection ct.?pls brif explaination about that.
what is power plant?
what is mean by xlpe cables?
what is general test conduted by transformer
Give some differences between open loop and closed loop?
How to calculate the 2500 Kva Transformer losses Primary 11KV Secondary 415volts
Post possible questions for Power Factor Panel FAT / SAT
Can any horizontally mounted motor be used as vertical?
I am getting above 60 V as open delta voltage against single phase unit ICT at tertiary delta formed and ICT getting trippped on NDR. ICT tested and found in order. PTs provided on tertiary are tested and in order. what may be the reason?
how the speed decreases of a generator in power station if load increases
Civil Engineering (5086)
Mechanical Engineering (4453)
Electrical Engineering (16638)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)