I did oil BDV test of 1600 KVA trafo 20KV/400V as per IEC
156. Result is 1) 58 KV 2) 58 KV 3)40 KV 4) 50 KV 5) 58 KV
6) 18 KV. Avr is 47 KV. Can we say oil is still ok even in
the 6th test BDV is 18 KV ?
Answer / k.prakashchandra
It is OK for voltages up to 170 KV.It appears that you did
not stir the oil properly during the last test.When in
doubt, it is always better to test another sample.
| Is This Answer Correct ? | 1 Yes | 0 No |
How many percent of power are not being registered if we bypass one side of the meter base terminal using #8 cu wire on 1-phase kwhr meter.
What is the RME and explain the full form and what is the RME work?
Why all voltage levels are the multiples of 11KV?
1.What is effect of capitance in transmission line? 2. After raising the voltage at receiving end what will be happen? 3.how we nullify or control the raised voltage at receiving end?
kVA rating of open delta connected transformer is _____% kVA rating of delta/delta connection A 50 B 70.7 C 57.7 D 75.7
Give atleast 20 alternating current apparatus and devices.
why D.C excitation is given to sunchronous motor?
can we check the resistance of earthing electrode while it is connected with the neutral of UPS system
flush point of transformer?
why secondary of open delta pt (two element pt) centre tap is earth what happen when this earth is removed
at which places we use 6.6KV Transformers and Motors
what is advantage of using star to delta in place of dol starter
Civil Engineering (5086)
Mechanical Engineering (4453)
Electrical Engineering (16638)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)